09-12-2011, 12:03 AM
Hi All,
I am having some problems with a MD11SR with blowing fuse F307 and bringing up fault code 35.
I had a look at the unit about 2 weeks ago with fault code 35 run circuit and found that fuse 307 had blown,
I checked the wiring and found the high pressure switch wire had rubbed through and was touching a pipe,
I repaired the wire and thought that would solve the problem, but today I had to go back to the unit and the same thing had happened again , fault 35 and fuse 307 blown.
I checked the wiring again briefly as it was blowing a gale and pouring down, but I couldn't see any other damaged wires.
Regards
Chris