View Full Version : Daikin chiller trouble



ah fai
05-12-2011, 06:54 AM
hi everybody.
i have a Daikin water cooled chiller with dual circuit (dual 60hp compressor), one of the circuit
not fully load. And i measure the system with FLUKE 52 Thermometer and the result is...

system 1 - liquid line before expansion valve 51deg C.
- after the expansion device 15.6deg C.
- discharge pressure 280psi
- suction pressure 80psi

system 2 - liquid line before expansion valve 49.3degC.
- after the expansion device 12.8deg C.
- discharge pressure 250psi
- suction pressure 66psi

thanks for advice...

install monkey
05-12-2011, 09:55 PM
whats the model number

ah fai
07-12-2011, 06:17 AM
i dont know the model, the info plate was gone, but i take a picture..
08383

Tesla
07-12-2011, 07:13 AM
Hi ah fai
You need to give us more and do your homework, we will need you to search this forum and you will see you need to take a lot more measurements like all temps (including water in/out and condenser on/off) etc and pressures - crank, liquid, discharge etc. Make sure your thermometer is accurate. What refrigerant? R22. The photo shows frost on the compressor - is this now or a previous photo? Tell us what you know of the history of this system then others can search and find this thread useful.