Has any one out there got a service manual for the above a/c. The unit runs for 10mins and stops. No alarm codes on pannel. Only a flashing led no.5 green/yellow. Thanks.

install monkey
03-12-2011, 12:08 PM
sent u e mail

stefs_cruiser
08-12-2011, 12:34 AM
I think it is actually nine minutes, and not ten....
And I suspect it will be your indoor coil sensor....

savoc
08-12-2011, 11:24 AM
thanks i will check it out.

assailant
08-12-2011, 02:37 PM
I think it is actually nine minutes, and not ten....


normally carry a stop watch on jobs? :D

stefs_cruiser
09-12-2011, 02:02 AM
I thought you guy’s in WA did, don’t you charge by the minute these days J


Seriously though, there is nothing in the firmware about 10 minutes, but the closest is that if the compressor runs for 9 minutes, and the indoor coil is below 2 degrees, it cycles the compressor off, without a fault code..

savoc
18-12-2011, 07:56 AM
Thanks for your help guys. Replaced the indoor coil sensor. unit is now working fine.