25-11-2011, 01:53 PM
Hello.

For a 12,000 BTU unit, is a capillary tube appropriate? If not, what type of expander is recommended for that?

Kompulsa
25-11-2011, 01:59 PM
Rotary Compressor:

DISPLACEMENT 21.6 cm3/rev

R22 Refrigerant.

Compression Ration: 8

PRESSURE DIFFERENCE AT
START-UP: There should be none.

If you need anything else from the datasheet, tell me.

stufus
25-11-2011, 03:11 PM
Either or whats the unit appliction, air con? refrigeration? medium or low temp? Room.? Display????
Cheers
Stu

Kompulsa
25-11-2011, 07:12 PM
Either or whats the unit appliction, air con? refrigeration? medium or low temp? Room.? Display????
Cheers
Stu

Room air conditioning. It will be used to chill water using a plain tubing evaporator, and then the chilled water will be circulated through a heat exchanger indoors that cools the air.

install monkey
25-11-2011, 08:27 PM
is this feeding 1 indoor heat exchanger? as a 12000btu unit capacity is 3.5kw,typically sized to cool a room of approx 40 sq mtr-so your trying to cool more than 1 room then ur compressor is gonna be chugging its nuts off!
go for tev as this will maintain superheat at different loads and give better control-even better go for an electronic expansion valve

Kompulsa
25-11-2011, 10:08 PM
It is for one room.

TEV means thermostatic expansion valve, right? :S

I remember asking for an expansion valve over the phone at the local refrigeration and A/C store. They quoted a price of a few thousand dollars (Jamaican) and didn't really ask for much information about the unit. Hopefully the only information they need is that I want a thermostatic expansion valve for a 12,000 BTU air conditioner? Or is there more I should confirm?

Brian_UK
25-11-2011, 11:14 PM
You have been given this link before...
http://www.sporlanonline.com/literature.shtml

May I suggest that you read some of it. ;)

Kompulsa
03-12-2011, 07:14 PM
Alright. When I called the store again they said the capillary tubing they have is for refrigerators, not air conditioners, and they didn't have the expansion valve for 12,000 BTU units, and ATL said they have capillary tubes for Panasonic units, but no expansion valve. They were like "what? Expansion valve for a 12,000 BTU?". There aren't any other expander options are there? Or will I be forced to pinch the tube and call that the expander like I did last time? :(

install monkey
03-12-2011, 07:26 PM
http://www.danfoss.com/NR/rdonlyres/CA5E4257-4F6B-4F41-A268-8CB4FE6874DD/0/PFA00A102.pdf

mikeref
03-12-2011, 09:45 PM
Kompulsa, this video may be helpful. http://www.youtube.com/watch?v=zWLYcJKHgB8

Kompulsa
13-12-2011, 04:45 PM
Thank you, I will watch that video in a moment. I have called quite a few stores and none of them have the capillary tube for 12,000 BTU units (in general, which is weird). How could that be.

install monkey
13-12-2011, 11:39 PM
just get a tev, it gives better control over varying loads, theres info on how to fit them, just remember to insulate the bulb,and mount the bulb lower than the tev head