Can someone please inform how to connect this compressor for 380/3ph/50 hz.
There is continuity between 1-4-7, 2-5-8, 3-6-9.The compressor has nine power terminals.The winding are okay and Megger readings to ground shows infinity.Thanks in advance.

Grizzly
22-11-2011, 07:20 PM
Maybe the attached will help?
There are 2 three phase options.
Part wind or D.O.L.
Grizzly

install monkey
22-11-2011, 07:52 PM
does the compressor leads have 2 contactors and a tiny orange delay timer then wire as part wind, if 3 contactors then its star delta configuration

goshen
22-11-2011, 08:46 PM
Hi
nice post grizzly .
best regards

chemi-cool
22-11-2011, 08:52 PM
You have 9 wires coming out not connected to any terminals?

Grizzly
22-11-2011, 10:12 PM
Thanks Goshen!

Chemi on the drawing I have attached it shows a link across 4,5 and 6.
Whereas on another which is to large to post it shows 4,5 and 6 as thermistor terminals.
That should be easy to prove by metering them out.
Grizzly.

Magoo
22-11-2011, 10:37 PM
Hi Grizzly,
a good post, the 9 terminals had me thinking. But being Carrier they would make them for any and every voltage option to standardize things.

mbc
22-11-2011, 11:25 PM
for 380 V /3 phase /50 HZ
1-4-7 is a one phase you say R or L1
2-5-8 is a second phase say S or L2
3-6-9 is a 3ed phase say T or L3

PaulZ
25-11-2011, 01:31 AM
Hi Grizzly
Good bit of info, I have saved it in our Carrier file, like Magoo 9 terminals had me wondering as well, thank you.
Paul

Grizzly
25-11-2011, 06:49 AM
Hi Guys.
It would seem there is a info gap where these comps are concerned.

Here is a Pocket Manual link (Which I have posted before )
Check out pages 112 and 113, all will be revealed!

http://www.carlylecompressor.com/Files/Carlyle_Compressor/Local/US-en/documents/020-611_withCover_LOWRES.pdf

If more detailed info is needed, you know where I am.
Grizzly

amarakbar
12-12-2011, 10:48 AM
Hi Grizzly,
Accept my belated thanks for the information. The compressor is now working okay. Thanks once again.