PDA

View Full Version : Daikin H4 Fault code



eire1
19-11-2011, 04:02 PM
Hey all. I'm due at a job in the morning with a Daikin showing a H4. Thanks to this site I found out that it's the Outdoor LP Switch.
Am I ok to loop it out to test to see if the switch itself is faulty?
Thanks

Grizzly
19-11-2011, 04:31 PM
Welcome Eire1.

Provided you put your gauges on to confirm you do not have a lp situation.
Logic would say a quick run would not harm.
Grizzly.

eire1
19-11-2011, 05:28 PM
Yeah, I'll see what kind of pressure I'm getting. It has to be the gas or switch itself really.
Thanks Grizzly

james10
19-11-2011, 06:51 PM
Could be the PCB thats faulty i've had that before

eire1
19-11-2011, 08:02 PM
I hope it's not the PCB. Sure I'll find out in the morning.

install monkey
19-11-2011, 10:11 PM
h4 -lp fault-ive had transducers fail,also ive got 1 with a lev not opening-not checked it properly yet

eire1
20-11-2011, 11:52 AM
No gas in the system at all. Hope this leak isn't too hard to find.