PDA

View Full Version : Qualitaire Heat Pump



garyjh24
17-11-2011, 11:37 PM
Hello,

Hope someone can help.

This is a wiring diagram from a split system heat pump Qualitaire. The unit Model No etc has worn so unfortunately I am unable to provide this information.

At present the unit is wired to cool only (connection C). The customer now wants to have it for heating also.

The unit is connected to an Eberle controller, which has the facility to provide 240volts to the reversing valve (connection RV). Do i need to provide a permanent 240 volt to the connection H for the defrost activation.

Please see picture. Thanks in advance8299

Brian_UK
17-11-2011, 11:50 PM
Sorry, where is connection 'H'?

install monkey
17-11-2011, 11:53 PM
found this on eaton williams website
ICU CONDENSING UNIT INSTALLATION MANUAL
September2003:E\Manuals\Others\Qualitair\ICC\0412118 8
6. POWER & CONTROL CONNECTIONS
ICU SINGLE PHASE COOLING ONLY
ICU Terminal Customer Connections
PE Customer Earth Connection
E
N Customer Neutral Connection
L Customer Live Connection
C Cooling Signal (From Indoor Unit)
S Motor speed control sensor
ICU SINGLE PHASE HEAT PUMP
ICU Terminal Customer Connections
PE Customer Earth Connection
E
N Customer Neutral Connection
L Customer Live Connection
C Cooling Signal (From Indoor Unit)
S Motor speed control sensor
RV Heating signal (from Indoor unit)
H Heating Signal (From Indoor Unit) – defrost heating.

hyperion
18-11-2011, 07:53 PM
Could it be that the terminal thought to be 'R' is actually 'H'.

garyjh24
20-11-2011, 10:54 PM
Sorry guys, the terminal marked as R should be H. That's what you get for posting at 23:37.Sorry.