View Full Version : Thermocold chiller alarm



Hvatit
04-11-2011, 04:55 PM
Hi.
I have a problem with chiller AWA ANERSAVE II 2260 ZC NT SE B R407c.
There is alarm "main fun/pump maintenance hour meter" wich I try to acknowledge but it appear again. The hour meter is 10013 hours. I can`t find any information in manual.
Is anybody know how to acknowledge this alarm?

stufus
04-11-2011, 11:34 PM
:DNever had an alarm from my fun pump
Sorry couldn't resist
Cheers
Stu

stufus
04-11-2011, 11:38 PM
The run hour threshold is set for 10,000 hours, you need to reset the run hours.
Unfortunately I'm not familiar with these chillers.
What make is the controller on it??
Cheers
Stu

NoNickName
05-11-2011, 04:55 PM
The reset in the maintenance branch of the microprocessor.
Enter with service password and reset hour counter.

goshen
05-11-2011, 05:39 PM
Hi
if it is a carel pco controller,
you indeed need to go to the maitenence menu and reset it there.
good luck

Hvatit
07-11-2011, 10:49 AM
The reset in the maintenance branch of the microprocessor.
Enter with service password and reset hour counter.
Thanks a lot.
It is Carel pCO1 controller.
I`ll try to find the service password. Maybe do you know?

Hvatit
07-11-2011, 12:24 PM
The problem has solved.
The password is 1234.
Thanks to "stufus", "goshen" and "NoNickName"

stufus
07-11-2011, 02:34 PM
Glad to hear it..
Cheers
Stu