PDA

View Full Version : Unit not heating very well



Kirky
01-11-2011, 11:13 AM
Hi all

Been called out to a Samsung inverter split system heat pump that isn't heating very well it's only doing 6 degree across indoor attached gauges and running at very low pressure 17 bar should be more like 35 bar in heating. Unit seems fine in cooling. With 15 Degree diff across evap cools room down in no time can only access unit a suction service port no other access port on system no so clued up on heat pumps was thinking sort on gas any other ideas

asmaircon
01-11-2011, 11:37 AM
Have you recovered the refrigerant to see how much you had in the system? could possibly be a low refrigerant level blowing out insufficient heat

savoc
01-11-2011, 11:47 AM
i would do the same as asmaircon.

Kirky
01-11-2011, 12:37 PM
That is exactly what I thought but the unit runs fine in cooling system pressure at 8 bar suction R410a if it was short on gas wouldn't I have low pressure in cooling also

chillerman2006
01-11-2011, 01:23 PM
Hi Kirky

have a look at attached, shame no discharge port though

R's chillerman

Kirky
01-11-2011, 02:06 PM
Thanks mate most helpful