PDA

View Full Version : carrier xarious 200 WITH STANDBY



charlie patt
29-10-2011, 07:24 PM
ao1 code up hp tested and useuall oil sep leaking changed and new drier please note there is a sporlan 103 on it not a carrier drier hp test overnight passed held 150 psi all night van at unit so vaced for 6 hrs vac pump steaming like a train but pulled to 29.903 VAC SWITCHED ON CONTROLLER TO CHECK EVAP FAN IN REAR AAND DRAW SOME HEAT AROUND THE EVAP THE VAC PUMP CHANGED NOTE AND WENT BACK TO POOR READING ON TORR GAUGE. I THOUGHT YOU DID NOT HAVE TO ENERGISE MAG VALVES ON THE CARRIER SMALL UNITS I ALWAYS DO ON THE BIG STUFF I DID CARRY OUT A FLOW CHECK AND IT WAS FINE SHOULD I FIT ME MAG VALVE LIFTER OR IS THERE A SEQUENCE ON THESE UNITS TO LIFT THROUGH CONTROLLER AT MO 8 CFM PUMP ON ALL NIGHT AND LIFTER ON DF COIL ANY ADVISE GUYS 2007 MODEL

clivemtk
30-10-2011, 11:48 AM
hot gas soleniod1 needs a magnet as it is closed

charlie patt
30-10-2011, 05:28 PM
does this valve open up on inital start up to level the pressures and i pressume due to one way valves it leaves a void of unvaced area in the unit thanks for help

tspgr
31-10-2011, 07:23 AM
Yes its opening at initial start but with the unit in vacuum it will never start by its self you will have a01 (lp switch) just put a magnet .......

Have a nice week.
Mixalhs greece