View Full Version : york controller ARTTHOO3S



fridge_bloke
07-10-2011, 03:54 PM
hi , i dont supose anyone has got any info on this controller,,operating and maintanance book would be really usefull.thanks in advance

chillerman2006
07-10-2011, 04:34 PM
Hi Fridge_bloke

what unit is it for ?

You might find it here

http://www.refrigeration-engineer.com/forums/showthread.php?32629-York-manuals-going-begging&highlight=

R's chillerman

fridge_bloke
07-10-2011, 06:50 PM
hi chillerman

wow, thats an extensive manual collection.il have a look through.the controller is off a clima roca / york system. i wanted to see the control capabilities of the controller.. currently there are 4 systems, 1 soh180-h condenser and 2 s1h090/120 evaps and 1 controler per system. as each evap is feeding a differant area of an indoor market im looking at ways of putting a control setpoint for each fancoil.if i cant do this from the existing controller im going to have to put an aditional pcb on the condenser and and aditional controller per system i guess

chillerman2006
07-10-2011, 07:24 PM
Hi Fridge_Bloke

that explains why I did not recongnise it

mine are all chiller manuals mate, dont have any for a/c sorry

R's chillerman

al
07-10-2011, 07:42 PM
Fridge bloke

With one condensing unit you'll need a common setpoint, the controller is basic enough, on/off heat cool and fan speed, you can tie the outdoor into a bms though and control the indoors through it.

al

fridge_bloke
07-10-2011, 08:39 PM
no worries chillerman


Hi al ,thanks ..im not sure if my garbled message before made sense.what our client wants is.....to operate the fancoils seperatly from each other and have there own setpoint.as the condenser has two independant fridge circuits i dont see why it shouldnt be possible

fb

al
07-10-2011, 09:14 PM
Check the outdoor, have you two sets of control boards? If so then you can control independently, mode must be the same for both.

some basic info:

http://unitary-europe.york.com/ingles/leaflets-2007-eng/SOC-SOH-K.pdf

for seperate setpoints wire a stat to each indoor, stat info here:

http://planning.bournemouth.gov.uk/OnlineRegister/Attachments/43757/Report_200781615320.pdf

They are not networkable and won't talk to each other, just basic control.

i think i have one in the van if you're stuck, i found that any generic heat pump controller did the same thing
and much easier to get.

al

fridge_bloke
08-10-2011, 09:09 AM
Cheers al, the york controller manual is a great help. it looks like il have to put an aditional lon board in each condenser along with an aditional controller to operate the fan coils.