View Full Version : Reach in cooler issues



nicksab
05-10-2011, 06:00 PM
hey everyone,

I am having issues with my display cooler

Symptoms: cooler not going any lower than 62F and txv valves /distributor icying upon both evaporators.

Measurements:

Refrigerant: R401A

suction line: 6 PSI @ 58F
liquid line : 90 PSI @ 80 F

according to R401A P/T chart,

superheat= 57F
subcooling= 5F

What s the cause of the problem? how can i fix it?

Thank you for your help

simon@parker
05-10-2011, 06:37 PM
air on the evap ?
air off ?
air on condenser ?
air off ?
would also check before you do any major investigation work has any new ac been fitted ?
does unit have a night blind ?
if it does pull it down see if it works then 60% of calls i used to attend were nothing to do with refrigeration probs but store conditions and air flow :)

Tayters
05-10-2011, 06:41 PM
Hi Nick,

From your figures subcooling normal/too low, superheat too high. System short of refrigerant.
Requires leak repair and recharge and make sure airflow through all coils (including condenser) is good.

Cheers,
Andy.

texas64
06-10-2011, 05:14 AM
I agree with Tayters. You are undercharged. Ball park pressures are around 25 psi suction, 150 psi liquid if the unit is indoors with 75 - 80 degree Fahrenheit temp. Find the leak, repair, recharge.