05-09-2011, 02:33 AM
I am working on sizing a blast cooler. I will take 3000 lbs of brisket @ 140 degrees down to 70 in 2 hours, then from 70 to below 40 in the next 4 hr.s . This program states I need to change my load factor number to ASHRAES standards. I don't have the book nor do they make it very clear which one it is I need. It is related to blast chilling/freezing product. Any help would be appreciated. I'd buy the book but I'm only working on a bid, not sure I'll even get the job. Thanks in advance.

Magoo
05-09-2011, 03:23 AM
Hi Freezon.
you will need high sensible heat ratio evaporators, low latent. Stops drying meat out. But get the deep meat temps low quickly. Is product hanging on hooks, blister packed, or on trays, or in boxes.
The hardest senario would be blister packs inside corragated boxes

Freezon
05-09-2011, 01:56 PM
The product is BBQ brisket & ribs. It will be on trays. It wont be concealed. It comes out of the smokers at 200 plus, is allowed to cool to 140 at ambients, then oof to the cooler to avoid thebacteria phase. I have been doing ths load calc program offered up from Trenton refrigeration products. They want to know the load factor, the default is 1. It tells you specifically if doing blast chiller or freezer, go to ASHRAE handbook of fundamentals and find it there. I toyed with the numbers and it made one heck of a difference. Also, It has options of changing humidity levels and TD's. Magoo, AM I looking to keep my humidty up arround 80% and TD at 7 to 9 degrees ? What I usually do is medium temp app and use electric defrost( basically freezer set up) to knock frozen moisture off coil and get back into the game. In the past I used my supply house engineer to help with these but lately I I cant afford to use him because I am at his mercy, dont know when I'll get it or if its accurate?

Magoo
06-09-2011, 01:42 AM
Hi Freezon,
I would be looking at ambient coolers for the first stage, then chiller for second stage, over size evaps for second stage for high humidity high SHR coils, cyclic air defrosts during pulldown in chiller section if necessary, with a system TD of 8 'F you should be fine.
Alternative, is blister pack each peice and put into chilled water bath, zero weight loss clients like that.

Magoo
06-09-2011, 02:46 AM
Hi Freezon,
by blister packs ,I mean nitrogen purged then vacuum sealed client product plastic wrappers. Zero bacteria, retains juices and flavours, self marinating, super tender. Shock chilled in zero degrees C water. Package then storage.

taz24
06-09-2011, 08:57 AM
The product is BBQ brisket & ribs. It will be on trays. It wont be concealed. It comes out of the smokers at 200 plus, is allowed to cool to 140 at ambients, then oof to the cooler to avoid thebacteria phase. I have been doing ths load calc program offered up from Trenton refrigeration products. They want to know the load factor, the default is 1. It tells you specifically if doing blast chiller or freezer, go to ASHRAE handbook of fundamentals and find it there. I toyed with the numbers and it made one heck of a difference. Also, It has options of changing humidity levels and TD's. Magoo, AM I looking to keep my humidty up arround 80% and TD at 7 to 9 degrees ? What I usually do is medium temp app and use electric defrost( basically freezer set up) to knock frozen moisture off coil and get back into the game. In the past I used my supply house engineer to help with these but lately I I cant afford to use him because I am at his mercy, dont know when I'll get it or if its accurate?



If the selection calculator is asking for blast chill or freezer loads, that is
because the specific heat content of products change when they are frozen.

If you are planning on pulling the temp down in 2 stages but if the end temp is
still above freezing then you need the fresh meat specific loads for that product.


<TABLE style="WIDTH: 336pt; BORDER-COLLAPSE: collapse" border=0 cellSpacing=0 cellPadding=0 width=448><COLGROUP><COL style="WIDTH: 48pt" span=7 width=64><TBODY><TR style="HEIGHT: 30pt; mso-height-source: userset" height=40><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; WIDTH: 48pt; HEIGHT: 62.25pt; BORDER-TOP: silver 1.5pt solid; BORDER-RIGHT: #cccccc 1pt solid" class=xl72 height=83 rowSpan=2 width=64>Food</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: #ffffcc; WIDTH: 144pt; BORDER-LEFT-COLOR: #cccccc; BORDER-TOP: silver 1.5pt solid; BORDER-RIGHT: #cccccc 1pt solid" class=xl74 width=192 colSpan=3>Specific Heat above Freezing</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: #ffff99; WIDTH: 144pt; BORDER-LEFT-COLOR: #cccccc; BORDER-TOP: silver 1.5pt solid; BORDER-RIGHT: silver 1.5pt solid" class=xl77 width=192 colSpan=3>Specific Heat below Freezing</TD></TR><TR style="HEIGHT: 32.25pt" height=43><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: #ffffcc; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 32.25pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl63 height=43 width=64>(Btu/lb<SUP>o</SUP>F)</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: #ffffcc; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl63 width=64>(KJ/kg<SUP>o</SUP>C)</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: #ffffcc; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl63 width=64>(Kcal/kg<SUP>o</SUP>C)</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: #ffff99; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl64 width=64>(Btu/lb<SUP>o</SUP>F)</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: #ffff99; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl64 width=64>(KJ/kg<SUP>o</SUP>C)</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: #ffff99; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl66 width=64>(Kcal/kg<SUP>o</SUP>C)</TD></TR><TR style="HEIGHT: 45.75pt" height=61><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 45.75pt; BORDER-RIGHT: #cccccc 1pt solid" class=xl67 height=61 width=64>Beef, carcass</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.68</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>2.85</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.68</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.48</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>2.01</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl68 width=64>0.48</TD></TR><TR style="HEIGHT: 30.75pt" height=41><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 30.75pt; BORDER-RIGHT: #cccccc 1pt solid" class=xl67 height=41 width=64>Beef, flank</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.56</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>2.34</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.56</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.32</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>1.34</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl68 width=64>0.32</TD></TR><TR style="HEIGHT: 30.75pt" height=41><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 30.75pt; BORDER-RIGHT: #cccccc 1pt solid" class=xl67 height=41 width=64>Beef, loin</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.66</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>2.76</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.66</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.35</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>1.47</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl68 width=64>0.35</TD></TR><TR style="HEIGHT: 30.75pt" height=41><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 30.75pt; BORDER-RIGHT: #cccccc 1pt solid" class=xl67 height=41 width=64>Beef, rib</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.67</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>2.81</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.67</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.36</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>1.51</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl68 width=64>0.36</TD></TR><TR style="HEIGHT: 30.75pt" height=41><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 30.75pt; BORDER-RIGHT: #cccccc 1pt solid" class=xl67 height=41 width=64>Beef, round</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.74</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>3.1</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.74</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.38</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>1.59</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl68 width=64>0.38</TD></TR><TR style="HEIGHT: 30.75pt" height=41><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 30.75pt; BORDER-RIGHT: #cccccc 1pt solid" class=xl67 height=41 width=64>Beef, rump</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.62</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>2.6</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.62</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.34</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>1.42</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl68 width=64>0.34</TD></TR><TR style="HEIGHT: 30.75pt" height=41><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 30.75pt; BORDER-RIGHT: #cccccc 1pt solid" class=xl67 height=41 width=64>Beef, shanks</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.76</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>3.18</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.76</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>0.39</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl65 width=64>1.63</TD><TD style="BORDER-BOTTOM: #cccccc 1pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl68 width=64>0.39</TD></TR><TR style="HEIGHT: 30.75pt" height=41><TD style="BORDER-BOTTOM: silver 1.5pt solid; BORDER-LEFT: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; HEIGHT: 30.75pt; BORDER-RIGHT: #cccccc 1pt solid" class=xl69 height=41 width=64>Beef, corned</TD><TD style="BORDER-BOTTOM: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl70 width=64>0.63</TD><TD style="BORDER-BOTTOM: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl70 width=64>2.64</TD><TD style="BORDER-BOTTOM: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl70 width=64>0.63</TD><TD style="BORDER-BOTTOM: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl70 width=64>0.34</TD><TD style="BORDER-BOTTOM: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: #cccccc 1pt solid" class=xl70 width=64>1.42</TD><TD style="BORDER-BOTTOM: silver 1.5pt solid; BACKGROUND-COLOR: transparent; BORDER-TOP-COLOR: #cccccc; WIDTH: 48pt; BORDER-LEFT-COLOR: #cccccc; BORDER-RIGHT: silver 1.5pt solid" class=xl71 width=64>0.34</TD></TR></TBODY></TABLE>

taz

.