View Full Version : How to assign thermodynamic properties after splitting two phase into gas and liquid
Looking at a simple TXV system. Lets assume after the TXV we seperate the gas down one pipe and the liquid down another. The question is how do we assign the correct thermodynamic properties to each fluid when it gets to end of its pipe.
The gas we want to do work on like heat it or compress it but before we can see where it ends up and predict its temperature and pressure we need to know from where we started? So do we move the gas out of the middle of the bell on a PH diagram to its edge and similarly do we move the liquid back to the saturated liquid line to gets its new properties?
Simply jumping out of the bell interior means that the enthalpy and entropy both make huge changes without any process being done. Hmmm
Your thoughts welcome
Chef
chillerman2006
19-08-2011, 11:15 PM
Looking at a simple TXV system. Lets assume after the TXV we seperate the gas down one pipe and the liquid down another. The question is how do we assign the correct thermodynamic properties to each fluid when it gets to end of its pipe.
The gas we want to do work on like heat it or compress it but before we can see where it ends up and predict its temperature and pressure we need to know from where we started? So do we move the gas out of the middle of the bell on a PH diagram to its edge and similarly do we move the liquid back to the saturated liquid line to gets its new properties?
Simply jumping out of the bell interior means that the enthalpy and entropy both make huge changes without any process being done. Hmmm
Your thoughts welcome
Chef
Gents, to save time & make ease of reading, Jump to; # 103
Just drop the txv & sounds like flooded plate heat exchangers with low pressure vessel, chilled water system, if you plot that on a chart it will come back as you described,
(other than that I am lost for what your trying to acheive)
The liquid remains in the heat exchangers, with some in the vessel, then the boiled of vapour is piped from the top of the vessel back to compressor
You can not get much work out of the vapour compared to the liquid, transfered to vapour
What are we trying to acheive ? :confused:
R's chillerman
install monkey
19-08-2011, 11:29 PM
i posed that question to "ask jeeves.com"(other similar sites are available)and the reply was-if u chop out the tev then each seperated pipe is going to p*ss out refrigerant.
chillerman2006
19-08-2011, 11:39 PM
i posed that question to "ask jeeves.com"(other similar sites are available)and the reply was-if u chop out the tev then each seperated pipe is going to p*ss out refrigerant.
I dont know for sure, you can not believe everything you hear on the net, (as tex found out) just asked the mrs though & she has confirmed "you would loose the gas & some oil"
(other than that I am lost for what your trying to acheive)
R's chillerman
So I split the gas and liquid but what h and s values are then given to each seperate flow. In a simple example lets have the evap at 1 bar and x=0.3
The gas/liquid is at h=231 and s=1.13 but now rip away the gas and suddenly it has a value of h=384 and an s=1.75 but we have not done anything except seperate the flows and we see a huge change in properties?
This means the gas/liquid together has one set of properties but when seperated they both have differant set of properties. What are the rules for reassigning the properties to each of the seperate streams.
Simply I want to know where to plot the 2 seperate streams on a PH diagram.
Chef
install monkey - seems Jeeves is way up to speed on this topic eh!
chillerman2006
20-08-2011, 12:03 AM
So I split the gas and liquid but what h and s values are then given to each seperate flow. In a simple example lets have the evap at 1 bar and x=0.3
The gas/liquid is at h=231 and s=1.13 but now rip away the gas and suddenly it has a value of h=384 and an s=1.75 but we have not done anything except seperate the flows and we see a huge change in properties?
This means the gas/liquid together has one set of properties but when seperated they both have differant set of properties. What are the rules for reassigning the properties to each of the seperate streams.
Simply I want to know where to plot the 2 seperate streams on a PH diagram.
Chef
chef
I am struggling here with what you mean & what your trying to achieve
As far as plotting the cycle on a chart, your vapour is to the right, your saturated vapour is in the middle & the liquid is to the left
but I cant see how this can be plotted without combining temperatures with pressure or why you would want to do this
chillerman2006
20-08-2011, 12:13 AM
A system needs to be balanced and an equilibrium from the energy transfering into an evaporator needs to balance out with the energy leaving the condensor, if you remove all vapour, what are we doing pumping neat liquid round a system (& as you mentioned) no work is being done
chillerman2006
20-08-2011, 12:20 AM
Energy can niether be created or destroyed just transfered from one form to another, with this in mind and my previous posts combined
The wheel has been created and the rules of thermodynamics are set in stone
My question is what are we trying to acheive ? (the impossible)
I dont understand :confused:
chillerman2006
20-08-2011, 01:24 AM
Come on chef
not many are like me & dont care what others think !
am not at this level, not at design level even
and do not see what benefit it is
this could be here a while as 60+ views already & nobody has a clue
mad fridgie
20-08-2011, 02:49 AM
Hi Chef, good to see you are looking into our little problem.
As far as enthalpy goes, if the vapor is just that vapour (full seperation) then the enthalpy will be on the saturation point of the curve. But how is entropy effected.???????
mad fridgie
20-08-2011, 02:50 AM
Come on chef
not many are like me & dont care what others think !
am not at this level, not at design level even
and do not see what benefit it is
this could be here a while as 60+ views already & nobody has a clue
The question is not based upon what you would expect!
chillerman2006
20-08-2011, 02:54 AM
Well chef
I could repeat all of what I have now been told & pretend I fully understand
But I have to work through some of it
I'll let you know I have been put on the right track though :)
utilizing the flash gas potential for generating flow through an evaporator
gaining maximum velocity through the evap coil which makes it 1 to 1 efficient
r's chillerman
mad fridgie
20-08-2011, 03:09 AM
well chef
i could repeat all of what i have now been told & pretend i fully understand
but i have to work through some of it
i'll let you know i have been put on the right track though :)
utilizing the flash gas potential for generating flow through an evaporator
gaining maximum velocity through the evap coil which makes it 1 to 1 efficient
r's chillerman
---------no--------
chillerman2006
20-08-2011, 03:26 AM
Well Mr Chef
I shall thank you for bringing this to my attention
I have and will continue to gain from this
As I said earlier I am not at this level
But will be following the progress & eagerly await the outcome
To see what can be acheived at such a level, I am yet to fully understand
And thankyou Mad for setting me straight, I can sleep now today
Good night Gents
chillerman2006
20-08-2011, 04:21 AM
Hi Chef, good to see you are looking into our little problem.
As far as enthalpy goes, if the vapor is just that vapour (full seperation) then the enthalpy will be on the saturation point of the curve. But how is entropy effected.???????
Mad
Maybe 4:00 here, I'm not sleeping till I have exhausted my understanding or lack of :)
Trying to understand here full seperation
And by this I mean on the chart the point of seperation I can see
With (as you said) enthalpy following the curve of saturation/vapour
enthalpy tails off at the point of the opposite curve saturation/liquid
So (correct me) this point where enthalpy tails of is the point of entropy
The point of diss-order prior to order and the point at which you need to achieve full seperation
If this is correct, how do you physically get to this point to acheive seperation in the first place ?
And how would this be put to use ?
What sort of system (design) if possible to get to this point & what would this acheive ?
mad fridgie
20-08-2011, 04:49 AM
Firstly read the first question, there is no mention of an evaporator.
So without thinking any further than what I say next
We have an open flash economiser vessel, liquid in, liquid out vapour out. what are the properties of all. Are there any strange things happening???
chillerman2006
20-08-2011, 04:53 AM
We have an open flash economiser vessel, liquid in, liquid out vapour out. what are the properties of all. Are there any strange things happening???
There is no stage of saturation
mad fridgie
20-08-2011, 04:58 AM
There is no stage of saturation
????????????????????
chillerman2006
20-08-2011, 04:59 AM
There is no stage of saturation
No there must be (surely) a point of saturation, just this is somehow minimal as you have found a way for full seperation
mad fridgie
20-08-2011, 05:07 AM
No there must be (surely) a point of saturation, just this is somehow minimal as you have found a way for full seperation
Yes seperation is an issue, but not the issue in hand (it must happen in an open flash vessel anyway) We are onlt talking about internal energy, (law of conservation)
chillerman2006
20-08-2011, 05:13 AM
????????????????????
There is stage of saturation, the point of entropy, where diss order becomes order once more , the point at which you achieve full seperation ??
chillerman2006
20-08-2011, 05:20 AM
I am following I am just trying to work out where we are tranfering the energy from and to - to enable enough to achieve this full seperation
mad fridgie
20-08-2011, 05:23 AM
high pressre liquid in (from cond) reduce pressure, what happens?
chillerman2006
20-08-2011, 05:25 AM
The liquid entering the flash econimiser has a specific heat/energy & at the point of seperation you are transfering the heat/energy from the liquid into the vapour, in effect subcooling the liquid
mad fridgie
20-08-2011, 05:33 AM
The liquid entering the flash econimiser has a specific heat/energy & at the point of seperation you are transfering the heat/energy from the liquid into the vapour, in effect subcooling the liquid
Not quite, apart from liquid head there is no sub cooling, and you are converting some liquid into vapour to keep the energy balanced. What then are actual properties of each exit stream. This is the question in hand?
chillerman2006
20-08-2011, 05:34 AM
The liquid entering the flash econimiser has a specific heat/energy by flashing of some lquid into vapour, you lower the pressure/temperature of the remaining liquid transfering the heat/energy to the vapour, subcooling the remaining liquid...
mad fridgie
20-08-2011, 05:39 AM
The liquid entering the flash econimiser has a specific heat/energy by flashing of some lquid into vapour, you lower the pressure/temperature of the remaining liquid transfering the heat/energy to the vapour, subcooling the remaining liquid...
You are cooling the liquid by vapourizing, the pressure has dropped, so the liquid is at saturation, hence is not sub cooled.
chillerman2006
20-08-2011, 05:59 AM
We have an open flash economiser vessel, liquid in, liquid out vapour out. what are the properties of all. Are there any strange things happening???
Liquid in - saturated liquid
liquid out - liquid only
vapour out - vapour only
neither are superheated or subcooled
& therefore
to go back to the question from Chef - #5
They would both be plotted on a ph chart along their respective lines at the point of saturation
???????????
mad fridgie
20-08-2011, 06:09 AM
Liquid in - saturated liquid
liquid out - liquid only
vapour out - vapour only
neither are superheated or subcooled
& therefore
to go back to the question from Chef - #5
They would both be plotted on a ph chart along their respective lines at the point of saturation
???????????
Yes one would think so?????, unless someone can show something else??? and this is all chef was asking
chillerman2006
20-08-2011, 06:20 AM
Thanks Mad
;)
I understand what you mean at last
Talk about - I beat around every bush first & need spoon feeding
Thanks Chef, if you had not have posted that question, there would still be that gap in my knowledge
;)
(But scrolling back up - no-one else came along and attempted it did they)
Back on track
So what you's were looking for was not me butting in, but someone on par with yourselves, who maybe could have come up with that something else that may or may not be there ?
mad fridgie
20-08-2011, 06:42 AM
no butting in is good, if you do not ask, then you will not get an answer. No one knows everything,
" the more I know, more I know, I know nothing"
chillerman2006
20-08-2011, 06:52 AM
no butting in is good, if you do not ask, then you will not get an answer. No one knows everything,
" the more I know, more I know, I know nothing"
Yeah, thanks Mate
Got a new signature too now
The methodology for solution will very much depend on the two-phase model you select. Flow regime for two-phase flow can be rather interesting & the theory is far from settled.
With different flow regimes, comes different levels of phase interaction.
So, pick a suitable model, or models, predict the flow regime & determine the appropriate properties.
I have a few very useful references to hand. If you pm me, with your current e-mail address, I'll get these onto you.
Chillerman, Mad is right and the whole question is just about how to get the properties of the split streams. If I read the previous posts correctly it seems it should be possible to simply move the 2 streams to their respective lines on the bubble but does that meet the no work and no heat input criteria is met. So I propose this:- (which is way too complicated for a Sunday morning I should add)
As no work or heat has been applied to either of the separated streams we can write the state function as
dS=dQ-dW
and the process as dh=dQ-dW+pdv+vdp
As dQ the heat input is zero and dW the work done is zero the dS must be zero
So x*S4-S3+S5-x*S5 = 0
And as both p the pressure and v the volume are constant dh can be set to zero so there is no gain or loss of enthalpy
So m*(h4-h3)-m*(1-x)*(h4-h5) = 0
Where h3 is the enthalpy at a quality of x
And h4 is the enthalpy at the gas line
And h5 is the enthalpy at the liquid line
Also S3, S4 and S5 are the entropy at the same locations.
This boils down to the fact if these state functions are equal to zero then we can indeed split the gas out and position directly on the gas line whilst the liquid must then be plotted on the liquid line with the caveat that both streams must have their respective masses carried with them and new processes can then be started.
But I am still mystified why the gas can have its entropy changed without work or heat input?
Chef
The methodology for solution will very much depend on the two-phase model you select. Flow regime for two-phase flow can be rather interesting & the theory is far from settled.
With different flow regimes, comes different levels of phase interaction.
So, pick a suitable model, or models, predict the flow regime & determine the appropriate properties.
I have a few very useful references to hand. If you pm me, with your current e-mail address, I'll get these onto you.
Thanks for the offer of the 2 phase papers but we really need to get to the pure gas and liquid states and the 2 phase episode is already past. There seems to be very little referance to this problem where ever I have looked.
Chef
chillerman2006
21-08-2011, 01:29 AM
Chillerman, Mad is right and the whole question is just about how to get the properties of the split streams. If I read the previous posts correctly it seems it should be possible to simply move the 2 streams to their respective lines on the bubble but does that meet the no work and no heat input criteria is met. So I propose this:- (which is way too complicated for a Sunday morning I should add)
As no work or heat has been applied to either of the separated streams we can write the state function as
dS=dQ-dW
and the process as dh=dQ-dW+pdv+vdp
As dQ the heat input is zero and dW the work done is zero the dS must be zero
So x*S4-S3+S5-x*S5 = 0
And as both p the pressure and v the volume are constant dh can be set to zero so there is no gain or loss of enthalpy
So m*(h4-h3)-m*(1-x)*(h4-h5) = 0
Where h3 is the enthalpy at a quality of x
And h4 is the enthalpy at the gas line
And h5 is the enthalpy at the liquid line
Also S3, S4 and S5 are the entropy at the same locations.
This boils down to the fact if these state functions are equal to zero then we can indeed split the gas out and position directly on the gas line whilst the liquid must then be plotted on the liquid line with the caveat that both streams must have their respective masses carried with them and new processes can then be started.
But I am still mystified why the gas can have its entropy changed without work or heat input?
Chef
Afternoon Chef
Thanks for such a detailed answer to work with,
(This is going to take me all day to get my head around as I have to reference all the letter symbols first, before i can attempt to work out what you mean.)
Morning MF
But I will, you's have me hooked now.
side tracking slightly away from the original reason for posting as i always look at the final acheivement
the research that you's are doing is for the design of 'A'
the problem i have is where they (liquid/vapour) end up and thus system balanceing
the component that does the system work has a limited ability
with this in mind
the more work it does removing the vapour from 'A'
the less work it can do in the usual way
ideally the liquid will be subcooled before it leaves 'A' moving it away from the bell
but it appears to me that this will reduce overall system ability to cool
and there is a fine line of how much vapour can be removed from 'A' without this reduction
I know you's must have already considered this so,
Just asking, can enough vapour be removed from the liquid to increase cooling without loosing cooling ability in the conventional way ?
mad fridgie
21-08-2011, 02:05 AM
Chef is in Fiji (Lucky bar stewerd), would I be working on refrigeration fomulures, or sucking dowm a Pina Colarda?
Good on chef for making the wrong choice.
CM, this not the process only the very beginning
chillerman2006
21-08-2011, 02:31 AM
Chef is in Fiji (Lucky bar stewerd), would I be working on refrigeration fomulures, or sucking dowm a Pina Colarda?
Good on chef for making the wrong choice.
CM, this not the process only the very beginning
Bar Steward, :confused:
When your hooked on info/solutions - yes the right choice!
All I could think of last night during dinner - when most would be thinking of serviceing:)
Oh well I will have to wait until your in a position to safely reveal
Am even more entreagued now - as i was thinking it could only be in one position on a conventional system, obviously much more to it,
Hope it all goes well next month :)
Your were right Mad and so we went to the sun deck and had a couple of Fiji Golds and the watched the world cup final and saw Brazil win 3 - 2. Exemplorary. Good input.
So the last test seems to be that h5-h3-x(h5+h4)+2xh3 must tend to zero to make
dh=d(S+pv) true.
But for this to happen it makes it an isochoric process and that then means that the gas portion at the outlet of the TXV already has the properties of the gas at the gas line. It is therefore only the liquid that holds the core thermodynamic properties. ie it does not matter what you do with the gas as it cannot affect the liquid except for normalising the mass if one removes it. Interesting!
How to calculate this on the fly and use it is a distant goal at the moment. But without it how can we go to stage 2.
Knickers, we are going back to the sun deck for some more Fiji Gold.
Chef
mad fridgie
21-08-2011, 05:58 AM
World cup???? Brazil???? Soccer???? (surely not that far behind the times????????)
Golds! yummmmmmmmmmmmm!
So it would seem that all we need to know at this point, is the % by mass of the lquid and vapour streams at the relevent saturation points?
mikeref
21-08-2011, 07:05 AM
Thanks Mad
;)
I understand what you mean at last
Talk about - I beat around every bush first & need spoon feeding
Thanks Chef, if you had not have posted that question, there would still be that gap in my knowledge
;)
(But scrolling back up - no-one else came along and attempted it did they)
Back on track
So what you's were looking for was not me butting in, but someone on par with yourselves, who maybe could have come up with that something else that may or may not be there ?
Have to chime in here, potential rant warning, and don't take it personally, but owning up to the fact that i've had to fight for every advancement in knowledge gained to date to succeed, not only in the refrigeration industry, as my main focus, but in my other curricular studies or hobbies i call them, including psychology and non mainstream medical advancements, that i struggle to digest the "quantum" aspect of this thread.. So continue, (giving the Jedi hand movement), and i will follow this thread through without asking questions and absorb what i can as it does trigger curiosity. Thanks "Mad" and C.M.;).. Mike.
Annular flow, slug flow, plug flow - all have vapour split from liquid. Take your pick.
You will need to understand the flow regime at some point, I fear. Thermodynamics will have assumptions about the fluid under consideration. Your final system will be somewhere between two extreme positions, due to liquid-vapour interaction.
chillerman2006
21-08-2011, 07:18 AM
Have to chime in here, potential rant warning, and don't take it personally, but owning up to the fact that i've had to fight for every advancement in knowledge gained to date to succeed, not only in the refrigeration industry, as my main focus, but in my other curricular studies or hobbies i call them, including psychology and non mainstream medical advancements, that i struggle to digest the "quantum" aspect of this thread.. So continue, (giving the Jedi hand movement), and i will follow this thread through without asking questions and absorb what i can as it does trigger curiosity. Thanks "Mad" and C.M.;).. Mike.
Good Evening Mike
You'll notice I did no contribution here mate,:eek: Have just found more I want to learn & comments keep the post up there, which may lead to another view from someone at their level
World cup???? Brazil???? Soccer???? (surely not that far behind the times????????)
Golds! yummmmmmmmmmmmm!
So it would seem that all we need to know at this point, is the % by mass of the lquid and vapour streams at the relevent saturation points?
It is the under 20 world cup held in Columbia and was live today.
I will work on the other stuff later.
chillerman2006
21-08-2011, 07:57 AM
I will work on the other stuff later.
Evening Chef
@ nearly 7pm more work, on a sunday, you must be due a few drinks now !
mad fridgie
21-08-2011, 09:51 AM
Hi Mike, please ask questions! As design engineers it is very easy to get an idea into our heads, and very difficult to remove. Hence the questions do seem to be vague, as we are looking for a different approach or answer. So please jump in as this can also help us re think our thoughts. What I am looking for is for proof that the widget will not work. or reversly that the widget may work.
Peter_1
21-08-2011, 09:56 AM
Just noticed now this post. I thought if Chef's asking a question and scrolling down, Mad Fridgie replies to it, then I have to read ever comma of this thread because both of them will dig very deep in the Thermodynamic laws again. Which I will do right now...reading, not digging.
mad fridgie
21-08-2011, 09:59 AM
Annular flow, slug flow, plug flow - all have vapour split from liquid. Take your pick.
You will need to understand the flow regime at some point, I fear. Thermodynamics will have assumptions about the fluid under consideration. Your final system will be somewhere between two extreme positions, due to liquid-vapour interaction.
Would the flow regime relate directly to the exit of the expansion valve and its effects reduce if the bell (liquid vapour seperator) is a reduced velocity and impegement type. (basically allowing the heavy liquid to fall to the bottom and the lighter vapour to rise to the top)
mad fridgie
21-08-2011, 10:09 AM
I am certainly not at the level chef, DesA or Peter, just a different level. I am always learning from these guys,(thank you), If you are unsure of what is being said. ask!, and no doubt we will try to answer in a different termonology.
Peter_1
21-08-2011, 10:17 AM
Come on chef
not many are like me & dont care what others think !
am not at this level, not at design level even
and do not see what benefit it is
this could be here a while as 60+ views already & nobody has a clue
This quote stands!!
mad fridgie
21-08-2011, 10:30 AM
This quote stands!!
For the quote to stand we have to make a start, and this is the start. Jumping straight into the process will only ask many more questions, than can be quickly answered.
Peter was is your opinion! what would be the properties of a seperated streams of flashed liquid.
mad fridgie
21-08-2011, 10:41 AM
I thinks it is time to bring Carters Widget into the open (against my peers advice, you know who are !!! lol)
Would the flow regime relate directly to the exit of the expansion valve and its effects reduce if the bell (liquid vapour seperator) is a reduced velocity and impegement type. (basically allowing the heavy liquid to fall to the bottom and the lighter vapour to rise to the top)
Basically separating & then forcing flow in a certain pattern. An interesting idea. Perhaps pipe diameter would play a useful part here?
Keep the liquid on the bottom part, with vapour sliding along the top part. There will be a critical vapour velocity at which surface waves will occur in the liquid - trying to re-introduce another more complicated flow pattern.
Keep below the critical velocity, or alter pipe diameter & we should be able to convey both separately. Thereafter, we can then treat Chef's problem from a thermodynamic point of view.
Ok, Chef. I've been re-reading your post.
Would you want to re-combine the separate flows, or keep them separate? If separate, then the thermo should be a little easier to resolve, I'd think. If re-combined, then flow regime will impact the final solution.
Can I suggest that we introduce some diagrams, then superimpose their thermodynamic states on the log(p)-h diagram?
If the two fluids remain at same pressure, then their properties ?will? lie on the same pressure line on the log(p)-h diagram - no? Their individual states should surely then move to liquid sat line & vapour sat lines respectively?
Interesting.
Peter_1
21-08-2011, 01:53 PM
To be honest, I explain this each year to my students. I take the fully expanded point on the refrigerant cycle where evaporation starts.
For me, the enthalpy of the gas and the liquid are there the same. Enthalpy can be found in charts and saturated tables (ST)
I then took the specific volume in the chart because you can't find those in the ST. For gas I took the value of both 'v' value on both sides of the saturated and multiplied this with the 'x' value, the lather found again in the chart.
For the liquid same but multiplying with 1-x.
DesA, isn't this a little bit the same conversation we once had via PM about something I didn't understand in the Dossat book Principles of Refrigeration?
I'm struggling also with the fact that a chart is a chart for a standstill refrigerant. But in a real life cycle, the refrigerant is flowing and then Bernouilli is coming around the corner. Then my brain starts to twist because I never studied thermodynamics really into its deep aspects and therefore, I can't combine a static situation with a flowing situation.
The compression process.. I had to study this the last in 1999 when I took my ATPL exams and we there had a complete course about jet engines, going really very deep into the theoretical side of a jet. I still remember I struggled with this one but anyhow, I made this one. There were +/- 130 out of 180 who had to go back a second time. I still have my exams about this course somewhere and if I re-read those now, it's far, so far away.
Chef, perhaps we should ask this once to real authorities in this field like Cengel , Boles, White,...
DesA, isn't this a little bit the same conversation we once had via PM about something I didn't understand in the Dossat book Principles of Refrigeration?
Good memory, Peter. :D
Chef, perhaps we should ask this once to real authorities in this field like Cengel , Boles, White,...
Would be lovely to invite them.
chillerman2006
21-08-2011, 05:06 PM
I thinks it is time to bring Carters Widget into the open (against my peers advice, you know who are !!! lol)
Definately NOT !
Apart of the thread I do fully Understand
Leave the widget in the can, We all are very curious obviously, but if this all works, curiousity will not kill the cat, but make him into a Fat Cat, if he has the ability to produce. And there are probaly many viewers to this site, some I suspect only viewing for this exact reason !
A few Red Herring's would not hurt though would they ! ;)
install monkey
21-08-2011, 05:15 PM
im not keen on herrings or most other fishies,i bet mad fridgies kids hate him when he drops hints of christmas prezzies in march!-if he's put time and money into such an item,he should test it,refine it then sell it and hopefully reap the rewards-so dont tell me what it is-keep the cat in the bag(it will die of starvation or asphixiation)-but can i buy a beta version of it and can i have a service manual for it and a few passwords to interogate it-not the dead cat!!!:o
chillerman2006
21-08-2011, 06:19 PM
the fact that a chart is a chart for a standstill refrigerant. But in a real life cycle, the refrigerant is flowing and then Bernouilli is coming around the corner.
we should ask this to real authorities in this field like Cengel , Boles, White,...
Evening Peter
Heisenberg's Uncertainty Principle, is also rearing his head (for me in more ways than one)
momentum = mass x velocity, the refrigerant has momentum p = mv, where 'p' is momentum, 'm' is mass and 'v' is velocity.
'Mass' can be considered as the amount of 'stuff' an object is made of. 'Velocity' is the component of the particle's speed acting in a specific, defined direction.
Basically the constant changing flow in a system, makes so many changes to your calculations (If I am understanding correctly so far) ??????
Evening Install,
Even though this is way beyond the premiership & way way beyond you & I, to start to understand the basics here of what is being said will be so valuable to us in the field, when the product is adventually released.
My miss-understandings are there with corrections from 'MF' & 'Chef', which should illiminate miss-conceptions for others.
A thread to be followed by everyone who wishes to understand how/what/why this product works
R's chillerman
chillerman2006
21-08-2011, 07:59 PM
This quote stands!!
"It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt."
These are both very true, But
If everyone is afraid to pipe up & make a fool of themselves, then none of us lesser knowledgible members will ever understand the concept & will not understand the system fully that we will be working on once it is released,
I'm quite happy to be branded, as long as I am learning, I win !
Would you not agree Sir ????
simon@parker
21-08-2011, 08:53 PM
"It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt
better to ask a stupid question than do a stupid thing because if you dont know its not stupid have told all the apprentices i have worked with that :) works as well :)
Peter_1
21-08-2011, 09:31 PM
"It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt."
These are both very true, But
If everyone is afraid to pipe up & make a fool of themselves, then none of us lesser knowledgible members will ever understand the concept & will not understand the system fully that we will be working on once it is released,
I'm quite happy to be branded, as long as I am learning, I win ! Would you not agree Sir ????
Agree for 100%. Hey, not Sir but Peter. PM me once your private email, I think there's a misunderstanding and I want to explain something.
Peter_1
21-08-2011, 10:06 PM
I wrote this afternoon Professor Boles. Will see if and what the man has to say us.
mad fridgie
21-08-2011, 10:41 PM
Definately NOT !
Apart of the thread I do fully Understand
Leave the widget in the can, We all are very curious obviously, but if this all works, curiousity will not kill the cat, but make him into a Fat Cat, if he has the ability to produce. And there are probaly many viewers to this site, some I suspect only viewing for this exact reason !
A few Red Herring's would not hurt though would they ! ;)
The fact is I can not get repeatable test results, so does the actual widget work or not.
I also technical limitations. and do not have the right set of quals to quantify the theory a proven principle. I now long have the finacial resources to employ those with the skills to take this to a theoretical and practical level. Plus after ecent expericiences, even when I developed other technologies it is just near impossible to sell the technology for any value, (I also buy a Lotto ticket)
So I either let is die and waste my money, or hope that some one picks it up, helps the industry, reduce energy use, loss my money. (with perhaps a honourable company who will thank MF with apalm full of silver for the idea, no that is dreaming)
chillerman2006
21-08-2011, 11:14 PM
The fact is I can not get repeatable test results, so does the actual widget work or not.
I also technical limitations. and do not have the right set of quals to quantify the theory a proven principle. I now long have the finacial resources to employ those with the skills to take this to a theoretical and practical level. Plus after ecent expericiences, even when I developed other technologies it is just near impossible to sell the technology for any value, (I also buy a Lotto ticket)
So I either let is die and waste my money, or hope that some one picks it up, helps the industry, reduce energy use, loss my money. (with perhaps a honourable company who will thank MF with apalm full of silver for the idea, no that is dreaming)
MF
I fully understand
You should be commended & indeed rewarded by who ever picks up your Idea for free
That is a 'very unselfish approach' to your current dilema
Mad, I take my hat off to you Sir.....much respect.....
& I hope very much that your other ventures in progress reward you to the extent you undoubtedly deserve.
Very Best Regards chillerman
ps. I removed my post from the other thread as so not to start confusing others
also I shall pm you my numbers & if I can do anything for you when in the UK, please give me a call.
So it would seem that all we need to know at this point, is the % by mass of the lquid and vapour streams at the relevent saturation points?
Interetsing question and an even more interesting outcome.
So the state equations seem to show the gas has no effect on the process of a 2 phase flow and therefore the corollary to this discussion so far is that the internal properties of say an evaporator can be described in fixed enthalpy values rather than a variable enthalpy.
Let me try and explain. After the TXV the value of h3 is known but as we move along the evaporator and more liquid evaporates to a gas the value of h changes and to define the properties at a new location we need to re-evaluate h from say a PH diagram.
But if we use the new equation
x=[dQ/dy*m-h4+h5]/(h4-h5)
we can now use fixed values of h namely those of the liquid line and gas line at the respective pressure. Now we can relate the fluid properties at any location with just heat input and do not need to revisit the PH diagram. The properties are defined by heat per unit length ie dQ/dy.
That would make calculations rather simpler in a 2 phase evaporator.
But this digresses from the original thread and just an interesting aside but should answer Mad's question? I think?
Chef
Mad – I am not sure that putting up widget #1 is your best idea. Better to solve the process issues which will then be public and other widgets may evolve along the way.
Widget #2 is not even close to being resolved yet.
Peter – very nice to see you here and I am not sure who Boles is but he sounds interesting and we await his thoughts.
There seems to be a lot of stuff needs to be done to fully understand the bell and the consequences of messing with it can be fruitful or a failure. So far the out come as noted in my last post is to relate the properties to fixed h points and that is significant from a computational point of view.
Chef
chillerman2006
22-08-2011, 02:57 AM
Good Afternoon Chef
I am still to fully get my head around your equations, but I will adventually:D
And if I am totally honest, my first thought of your post, was this is a wind up !
Quite clearly not - Just at a level far beyond most
R's chillerman
mad fridgie
22-08-2011, 03:12 AM
Mad – I am not sure that putting up widget #1 is your best idea. Better to solve the process issues which will then be public and other widgets may evolve along the way.
Widget #2 is not even close to being resolved yet.
Peter – very nice to see you here and I am not sure who Boles is but he sounds interesting and we await his thoughts.
There seems to be a lot of stuff needs to be done to fully understand the bell and the consequences of messing with it can be fruitful or a failure. So far the out come as noted in my last post is to relate the properties to fixed h points and that is significant from a computational point of view.
Chef
Hi chef, I did have to think hard about what i was going to give, but after the last few attempts at commercialization, on other ideas, (which were somewhat easier, to prove, build and test) i have decided to cut my losses, enjoy the ride. i have been in contact with one of the big multi-national component manufactures, who showed interest, only if i could front with a full working prototype and the theorectical calculations to back other selections. They would then look at the manufacture and marketting
At this time more than i am willing and can afford to risk.
To be truthful it is not an exiting enough product/idea for venture capalists
Good Afternoon Chef
I am still to fully get my head around your equations, but I will adventually:D
And if I am totally honest, my first thought of your post, was this is a wind up !
Quite clearly not - Just at a level far beyond most
R's chillerman
Chillerman this is not a wind up but serious stuff that Mad and I have been discussing for a long time without a conclusion so we thought to open it up and see if others could input some ideas. You have made several comments that are useful so that part is working - solved no - but a few more ideas to help us resolve it.
All it takes is just one comment so keep tweeting away.
Chef
Hi chef, I did have to think hard about what i was going to give, but after the last few attempts at commercialization, on other ideas, (which were somewhat easier, to prove, build and test) i have decided to cut my losses, enjoy the ride. i have been in contact with one of the big multi-national component manufactures, who showed interest, only if i could front with a full working prototype and the theorectical calculations to back other selections. They would then look at the manufacture and marketting
At this time more than i am willing and can afford to risk.
To be truthful it is not an exiting enough product/idea for venture capalists
Well maybe when I finally get to NZ we can sit down with the back of a fag packet and sort this all out. It needs to sorted one way or the other as it is too interesting.
mad fridgie
22-08-2011, 07:23 AM
fag packet (s), now thats what i call a real design tool.
PS
NOT an homosexual packet, cigerette packet (for our north american friends)
I'd like to introduce the basic laws of thermodynamics, to clear up the discussion a little:
http://en.wikipedia.org/wiki/Thermodynamics
If a system is in thermodynamic equilibrium and is not subject to an externally imposed force field, such as gravity, electricity, or magnetism, then (subject to a proviso stated in the following sentence) it is homogeneous, that is say, spatially uniform in all respects.[48] There is a proviso here; a system in thermodynamic equilibrium can be inhomogeneous in the following respect: it can consist of several so-called 'phases', each homogeneous in itself, in immediate contiguity with other phases of the system, but distinguishable by their having various respectively different physical characters; a mixture of different chemical species is considered homogeneous for this purpose if it is physically homogeneous.[49] For example, a vessel can contain a system consisting of water vapour overlying liquid water; then there is a vapour phase and a liquid phase, each homogeneous in itself, but still in thermodynamic equilibrium with the other phase. For the immediately present account, systems with multiple phases are not considered, though for many thermodynamic questions, multiphase systems are important.
So, the moment the vapour & liquid are 'physically separated e.g. by a wall, then they can be considered in isolation, with their own states. Once separated, thermodynamic theory would then instruct you to place the new state point at its pressure/temp/enthalpy/entropy value. In some cases, the point seems allowed to 'jump' to its new position.
Perhaps we can now explore this via thermodynamic diagrams, Chef. (Very interesting thread. Making me think a fair bit... )
:)
Peter_1
22-08-2011, 09:46 AM
Peter – very nice to see you here and I am not sure who Boles is but he sounds interesting and we await his thoughts.
This will clarify
http://books.google.com/books/about/Thermodynamics.html?id=5-hSAAAAMAAJ
mikeref
22-08-2011, 11:53 AM
fag packet (s), now thats what i call a real design tool.
PS
NOT an homosexual packet, cigerette packet (for our north american friends)
TO clarify further: Fag packet, meaning, packet of taylor made smokes or factory made cigarettes, as opposed to "Rollies", where one has to roll your own, and generally don't include a filter. Note: roll your own means pulling strands of ready rubbed tobacco and rolling into formation prior to placing into specific paper, such as the brand, "tally ho" than, with desired thickness, and some skill, manage to seal the deal and light the end while sucking on the other... Others, who choose to to roll funny weed will have this skill mastered. please... continue. . hand movement similar to Jedi master. Move along.
I'd like to introduce the basic laws of thermodynamics, to clear up the discussion a little:
http://en.wikipedia.org/wiki/Thermodynamics
So, the moment the vapour & liquid are 'physically separated e.g. by a wall, then they can be considered in isolation, with their own states. Once separated, thermodynamic theory would then instruct you to place the new state point at its pressure/temp/enthalpy/entropy value. In some cases, the point seems allowed to 'jump' to its new position.
Perhaps we can now explore this via thermodynamic diagrams, Chef. (Very interesting thread. Making me think a fair bit... ):)
OK we are both on the exact same page and 'jumping' to a new position with new properties seems to be possible but there is no precedence or rules as of yet.
The thermodynamic relations I proposed earlier seem to show this jump is supported for isobaric and isochoric processes but may only work for specific circumstances. What is the general form of the equations that allow us to jump to any part of the bell still keeping p and T constant?
So what have you found for a process at the moment that may take us forward?
Thanks
Chef
So here is a PH diagram of a 4 stage drop with phase seperation. To keep it simple I have started at h2 at the outlet of the condenser and ended up at h3-4 at the inlet to the evaporator. At each location after a stage drop the phases are split into their gas and liquid forms and repositioned on the PH diagram to relevant gas or liquid line.
This is a very basic start at suggesting a process to discuss further and obvious errors include gas that has been removed at stage 1, 2 and 3 are cooled to the final evap temperature and the process should follow an isenthalpic drop but maybe we can include that at version 2 of the diagram.
Now we have the same (actually more cooling effect) cooling as a one stage drop but several gas flows at intermedite pressures that can do work. Enter the Carter Widget.
Any comments so far?
Chef7134
mad fridgie
23-08-2011, 12:48 AM
The question then begs, when we have our various vapour streams, at different pressures (which has very little practical use in the net cooling effect) is how we can utalise the ? (being vague on purpose) to increase the pressure at the compressor suction without restricting flow in the evaporator.
What is the best possible theorectrical out come
Well I presume a multi ring expander with each concentric ring sized correctly for the pressure input and flow rate to combine the flows and then use the suction provided to reduce the last section of flash gas and lower its pressure and temperature and hence get more cooling. then the final gas goes to the compressor and combines with the evap gas. Seems logical.
mad fridgie
23-08-2011, 03:16 AM
Well I presume a multi ring expander with each concentric ring sized correctly for the pressure input and flow rate to combine the flows and then use the suction provided to reduce the last section of flash gas and lower its pressure and temperature and hence get more cooling. then the final gas goes to the compressor and combines with the evap gas. Seems logical.
that is the problem, "it just seems logical", but somewhere in the back of mind, i feel the "Murphy effect" maybe present, the guy who trips you up at the end!
Because it is so logical, surely someone else must of been down this track?
Maybe you missed my point so I will try again. We have removed gas at the 8 bar line and so this gas is no longer cooled by flashing liquid, similarly the gas at 4 and 2 bar are seperated and they also need no further cooling. In a standard TXV system all the gas is cooled to the evap temp so we have saved some energy here. The question is - is it enough to help and then we have the side streams of gas.
Got to replace the mainsail so the diagram will come later.
Chef
mad fridgie
23-08-2011, 04:34 AM
I understand, each proportion that is removed no longer requires the sensible energy removed. to the next stage.
Each stage then will have a greater amount of potential energy to be used for work. Whilst increasing the actual liquid mass flow to the evap (less total flash gas produced). Struggling in how to manufacture cheaply for small to medium systems, larger becomes much easier. (maybe this where it should be?)
The savings in liquid flashing off to cool the gas is the first part. You seem to like that bit and then something like a deLaval nozzle, they can be multi ringed concentric and have nice thermo properties. Small system is a financial problem but medium would be OK. Large systems would definetly use a compander to extract the energy sucked out of the flash gas but that is known technology for decades in the cryogenic industry so not new by an means.
To get the theory of this nailed is huge - really huge so may be a while till this thread gets a final answer unless someone pops up with a neat idea!!! Still I love a challenge.
Chef
chillerman2006
23-08-2011, 02:07 PM
Chillerman this is not a wind up but serious stuff that Mad and I have been discussing for a long time without a conclusion so we thought to open it up and see if others could input some ideas. You have made several comments that are useful so that part is working - solved no - but a few more ideas to help us resolve it.
All it takes is just one comment so keep tweeting away.
Chef
Thankyou Chef
I take that as a massive compliment, coming from someone at your level
R's chillerman
Maybe you missed my point so I will try again. We have removed gas at the 8 bar line and so this gas is no longer cooled by flashing liquid, similarly the gas at 4 and 2 bar are seperated and they also need no further cooling. In a standard TXV system all the gas is cooled to the evap temp so we have saved some energy here. The question is - is it enough to help and then we have the side streams of gas.
Got to replace the mainsail so the diagram will come later.
Chef
I'm confused. Does the liquid cool the gas?... or does the gas cool the liquid?
chillerman2006
23-08-2011, 06:51 PM
This will clarify
http://books.google.com/books/about/Thermodynamics.html?id=5-hSAAAAMAAJ
Peter
Are any of these recommended purchases for my self, or a level I can not reach ???
R's chillerman
chillerman2006
23-08-2011, 07:16 PM
I'm confused. Does the liquid cool the gas?... or does the gas cool the liquid?
Hi Gary
If I have followed properly, the liquid is cooled by the drop in pressure after the condensor, before the vessel, (constant pressure valve) the flash gas removal, does not affect 'p' or 't' but increase's mass to txv
Regards Chillerman
OK we are both on the exact same page and 'jumping' to a new position with new properties seems to be possible but there is no precedence or rules as of yet.
The thermodynamic relations I proposed earlier seem to show this jump is supported for isobaric and isochoric processes but may only work for specific circumstances. What is the general form of the equations that allow us to jump to any part of the bell still keeping p and T constant?
So what have you found for a process at the moment that may take us forward?
Thanks
Chef
Ok, Chef. So you're looking for the 'jump' condition inherent within the equations - rather than simply taking for granted that the fluid 'has to' jump when split into vapour & liquid.
Let me look a little more into the equations for the 'jump' condition. Never so easy, but it should surely be there to justify the change. (I love jump conditions... :)
Hi Gary
If I have followed properly, the liquid is cooled by the drop in pressure after the condensor, before the vessel, (constant pressure valve) the flash gas removal, does not affect 'p' or 't' but increase's mass to txv
Regards Chillerman
Actually, on a drop in pressure part of the liquid flashes into vapor and heat from the liquid is transferred to that vapor... the gas cools the liquid.
chillerman2006
23-08-2011, 09:24 PM
Actually, on a drop in pressure part of the liquid flashes into vapor and heat from the liquid is transferred to that vapor... the gas cools the liquid.
Hi Gary
Thankyou Sir,
Dont know what I was thinking trying to educate you, duh!
The info hit a reverse cycle valve & miss-directed
But still got you thinking, mate & now we both understand,
R's chillerman
Actually, on a drop in pressure part of the liquid flashes into vapor and heat from the liquid is transferred to that vapor... the gas cools the liquid.
So a small experiment is due here I feel. I pour lighter fuel on my hand and as it evaporates it gets cold, if I blow on it it gets even colder as more evaporation takes place. So you are telling me that the gas after evaporation is cold and in the time available before it disperses in the atmosphere it has time to transfer it coldness to the liquid. Yeah right I beleive that. If you wish you could provide a useful referance to support your comments.
In the PH diagram I posted there are 3 places where we propose to strip the gas away and pipe it off for its own process. The first split is at 8 bar which is 31.4C so the gas remains at that temp in its side pipe.
If we had left that gas with the rest of the refrigerant as in a standard TXV system it would need to be cooled down to -26C which is the evap temp in this case.
So we are going to need to cool that gas and the only source of 'cold' is the liquid hence my comment the liquid will cool the gas. The JT effect is not enough on its own. It is the phase transition that does the cooling.
But you say the gas cools the liquid so by dropping some gas from 8 bar to 1 bar it will cool in a process that not not only cools itself but has enough (negative) energy to also cool some of the liquid. ????
Chef
mad fridgie
23-08-2011, 10:00 PM
Actually, the liquid cools the liquid.
Liquid at saturation, "no gas/vapour" so how can the gas cool he liquid.
Part of the liquid stream absorbs energy for the remainder of the liquid stream, for the correct amount of energy to be absorbed, (to reach balance) then some of the liquid has to convert into vapour(gas). The gas/vapour is a "by product". of the process. "It is the conversion" of state
I would say that the choice of word "cool" is incorrect.
Actually, in the transformation of liquid to vapor, heat energy is transferred from the liquid to the vapor... so... the vapor cools the liquid.
mad fridgie
23-08-2011, 10:32 PM
Actually, in the transformation of liquid to vapor, heat energy is transferred from the liquid to the vapor... so... the vapor cools the liquid.
If the vapour does not exist, then it can not do any work. Yes it is the transformation, the new formed vapour holds the energy. No energy is transfered to the vapour after the vapour is formed, so the vapour can not cool the liquid.
Open a valve on the top of a refrigerant container. Vapor boils off and the liquid on the bottom gets very cold. Where did it's heat energy go to? It is contained in the escaping vapor.
mad fridgie
23-08-2011, 10:58 PM
Open a valve on the top of a refrigerant container. Vapor boils off and the liquid on the bottom gets very cold. Where did it's heat energy go to? It is contained in the escaping vapor.
Yes the vapour hold the energy of transformation which gives the "impression" that the vapour must of cooled the liquid. For the vapour to cool the liquid, then for heat transfer to occur the liquid has to be warmer than the vapour (vapour has to be colder than the liquid).
I supose to be factual; it is the change in pressure that cools the liquid by method of liquid to vapour transformation
If the vapour does not exist, then it can not do any work. Yes it is the transformation, the new formed vapour holds the energy. No energy is transfered to the vapour after the vapour is formed, so the vapour can not cool the liquid.
Okay... I'll buy that.
Okay... I'll buy that.
Good so we all agree the cooling effect comes from the latent heat of vapourisation.
So back to the point how much energy do we save by not cooling the seperated gas flows?
mad fridgie
24-08-2011, 12:06 AM
On R134a 50SCT and -30SST no sub cooling
3 takes off
30C
10C
-10C
between 9-10% extra net cooling for the same liquid mass flow
I also make it 9% and we still have usefull work that the gas can do.
So next how much energy do we have in the 3 streams. Lets start with the theoretical amount and then we can reduce it by an efficiency dependant on which method id used to gain that energy.
Chef
mad fridgie
24-08-2011, 03:40 AM
I also make it 9% and we still have usefull work that the gas can do.
So next how much energy do we have in the 3 streams. Lets start with the theoretical amount and then we can reduce it by an efficiency dependant on which method id used to gain that energy.
Chef
I will work out, using my chosen method, but will wait till others show their method (not a cop out). I do not want to influence how the following calculations are made. I feel that my method maybe flawed, even though the method does seem plausable to me?
chillerman2006
24-08-2011, 07:29 AM
So I was right then, Jedi Master
:D
R's chillerman
chillerman2006
24-08-2011, 06:23 PM
Chef,
I hope you dont mind, a small contribution to make this a little easier for 'yous' to quantify
Originally Posted by Chef
Looking at a simple TXV system. Lets assume after the TXV we seperate the gas down one pipe and the liquid down another. The question is how do we assign the correct thermodynamic properties to each fluid when it gets to end of its pipe.
The gas we want to do work on like heat it or compress it but before we can see where it ends up and predict its temperature and pressure we need to know from where we started? So do we move the gas out of the middle of the bell on a PH diagram to its edge and similarly do we move the liquid back to the saturated liquid line to gets its new properties?
Simply jumping out of the bell interior means that the enthalpy and entropy both make huge changes without any process being done. Hmmm
Your thoughts welcome
Originally Posted by Chef
So I split the gas and liquid but what h and s values are then given to each seperate flow. In a simple example lets have the evap at 1 bar and x=0.3
The gas/liquid is at h=231 and s=1.13 but now rip away the gas and suddenly it has a value of h=384 and an s=1.75 but we have not done anything except seperate the flows and we see a huge change in properties?
This means the gas/liquid together has one set of properties but when seperated they both have differant set of properties. What are the rules for reassigning the properties to each of the seperate streams.
Simply I want to know where to plot the 2 seperate streams on a PH diagram.
Chef
Originally Posted by chillerman2006
chef
As far as plotting the cycle on a chart, your vapour is to the right, your saturated vapour is in the middle & the liquid is to the left
but I cant see how this can be plotted without combining temperatures with pressure or why you would want to do this
Originally Posted by mad fridgie
Hi Chef, good to see you are looking into our little problem.
As far as enthalpy goes, if the vapor is just that vapour (full seperation) then the enthalpy will be on the saturation point of the curve. But how is entropy effected.???????
Originally Posted by mad fridgie
The question is not based upon what you would expect!
Originally Posted by mad fridgie
Firstly read the first question, there is no mention of an evaporator.
So without thinking any further than what I say next
We have an open flash economiser vessel, liquid in, liquid out vapour out. what are the properties of all. Are there any strange things happening???
Originally Posted by mad fridgie
Yes seperation is an issue, but not the issue in hand (it must happen in an open flash vessel anyway) We are onlt talking about internal energy, (law of conservation)
Originally Posted by mad fridgie
high pressre liquid in (from cond) reduce pressure, what happens?
Originally Posted by mad fridgie
Not quite, apart from liquid head there is no sub cooling, and you are converting some liquid into vapour to keep the energy balanced. What then are actual properties of each exit stream. This is the question in hand?
Originally Posted by mad fridgie
You are cooling the liquid by vapourizing, the pressure has dropped, so the liquid is at saturation, hence is not sub cooled.
Originally Posted by chillerman2006
Liquid in - saturated liquid
liquid out - liquid only
vapour out - vapour only
neither are superheated or subcooled
& therefore
to go back to the question from Chef - #5
They would both be plotted on a ph chart along their respective lines at the point of saturation
???????????
Originally Posted by mad fridgie
Yes one would think so?????, unless someone can show something else??? and this is all chef was asking
Originally Posted by desA
The methodology for solution will very much depend on the two-phase model you select. Flow regime for two-phase flow can be rather interesting & the theory is far from settled.
With different flow regimes, comes different levels of phase interaction.
So, pick a suitable model, or models, predict the flow regime & determine the appropriate properties.
I have a few very useful references to hand. If you pm me, with your current e-mail address, I'll get these onto you.
Originally Posted by Chef
Chillerman, Mad is right and the whole question is just about how to get the properties of the split streams. If I read the previous posts correctly it seems it should be possible to simply move the 2 streams to their respective lines on the bubble but does that meet the no work and no heat input criteria is met. So I propose this:- (which is way too complicated for a Sunday morning I should add)
As no work or heat has been applied to either of the separated streams we can write the state function as
dS=dQ-dW
and the process as dh=dQ-dW+pdv+vdp
As dQ the heat input is zero and dW the work done is zero the dS must be zero
So x*S4-S3+S5-x*S5 = 0
And as both p the pressure and v the volume are constant dh can be set to zero so there is no gain or loss of enthalpy
So m*(h4-h3)-m*(1-x)*(h4-h5) = 0
Where h3 is the enthalpy at a quality of x
And h4 is the enthalpy at the gas line
And h5 is the enthalpy at the liquid line
Also S3, S4 and S5 are the entropy at the same locations.
This boils down to the fact if these state functions are equal to zero then we can indeed split the gas out and position directly on the gas line whilst the liquid must then be plotted on the liquid line with the caveat that both streams must have their respective masses carried with them and new processes can then be started.
But I am still mystified why the gas can have its entropy changed without work or heat input?
Chef
Originally Posted by Chef
Your were right Mad and so we went to the sun deck and had a couple of Fiji Golds and the watched the world cup final and saw Brazil win 3 - 2. Exemplorary. Good input.
So the last test seems to be that h5-h3-x(h5+h4)+2xh3 must tend to zero to make
dh=d(S+pv) true.
But for this to happen it makes it an isochoric process and that then means that the gas portion at the outlet of the TXV already has the properties of the gas at the gas line. It is therefore only the liquid that holds the core thermodynamic properties. ie it does not matter what you do with the gas as it cannot affect the liquid except for normalising the mass if one removes it. Interesting!
How to calculate this on the fly and use it is a distant goal at the moment. But without it how can we go to stage 2.
Chef
Originally Posted by mad fridgie
So it would seem that all we need to know at this point, is the % by mass of the lquid and vapour streams at the relevent saturation points?
Originally Posted by Peter_1
Just noticed now this post. I thought if Chef's asking a question and scrolling down, Mad Fridgie replies to it, then I have to read ever comma of this thread because both of them will dig very deep in the Thermodynamic laws again. Which I will do right now...reading, not digging.
Originally Posted by desA
Annular flow, slug flow, plug flow - all have vapour split from liquid. Take your pick.
You will need to understand the flow regime at some point, I fear. Thermodynamics will have assumptions about the fluid under consideration. Your final system will be somewhere between two extreme positions, due to liquid-vapour interaction.
Originally Posted by mad fridgie
Would the flow regime relate directly to the exit of the expansion valve and its effects reduce if the bell (liquid vapour seperator) is a reduced velocity and impegement type. (basically allowing the heavy liquid to fall to the bottom and the lighter vapour to rise to the top)
Originally Posted by mad fridgie
I am certainly not at the level chef, DesA or Peter, just a different level. I am always learning from these guys,(thank you), If you are unsure of what is being said. ask!, and no doubt we will try to answer in a different termonology.
Originally Posted by desA
Basically separating & then forcing flow in a certain pattern. An interesting idea. Perhaps pipe diameter would play a useful part here?
Keep the liquid on the bottom part, with vapour sliding along the top part. There will be a critical vapour velocity at which surface waves will occur in the liquid - trying to re-introduce another more complicated flow pattern.
Keep below the critical velocity, or alter pipe diameter & we should be able to convey both separately. Thereafter, we can then treat Chef's problem from a thermodynamic point of view.
Originally Posted by desA
Ok, Chef. I've been re-reading your post.
Would you want to re-combine the separate flows, or keep them separate? If separate, then the thermo should be a little easier to resolve, I'd think. If re-combined, then flow regime will impact the final solution.
Can I suggest that we introduce some diagrams, then superimpose their thermodynamic states on the log(p)-h diagram?
If the two fluids remain at same pressure, then their properties ?will? lie on the same pressure line on the log(p)-h diagram - no? Their individual states should surely then move to liquid sat line & vapour sat lines respectively?
Interesting.
Originally Posted by Peter_1
To be honest, I explain this each year to my students. I take the fully expanded point on the refrigerant cycle where evaporation starts.
For me, the enthalpy of the gas and the liquid are there the same. Enthalpy can be found in charts and saturated tables (ST)
I then took the specific volume in the chart because you can't find those in the ST. For gas I took the value of both 'v' value on both sides of the saturated and multiplied this with the 'x' value, the lather found again in the chart.
For the liquid same but multiplying with 1-x.
DesA, isn't this a little bit the same conversation we once had via PM about something I didn't understand in the Dossat book Principles of Refrigeration?
I'm struggling also with the fact that a chart is a chart for a standstill refrigerant. But in a real life cycle, the refrigerant is flowing and then Bernouilli is coming around the corner. Then my brain starts to twist because I never studied thermodynamics really into its deep aspects and therefore, I can't combine a static situation with a flowing situation.
The compression process.. I had to study this the last in 1999 when I took my ATPL exams and we there had a complete course about jet engines, going really very deep into the theoretical side of a jet. I still remember I struggled with this one but anyhow, I made this one. There were +/- 130 out of 180 who had to go back a second time. I still have my exams about this course somewhere and if I re-read those now, it's far, so far away.
Chef, perhaps we should ask this once to real authorities in this field like Cengel , Boles, White,...
Originally Posted by desA
Good memory, Peter. :D
Would be lovely to invite them.
Originally Posted by chillerman2006
Evening Peter
Heisenberg's Uncertainty Principle, is also rearing his head (for me in more ways than one)
momentum = mass x velocity, the refrigerant has momentum p = mv, where 'p' is momentum, 'm' is mass and 'v' is velocity.
'Mass' can be considered as the amount of 'stuff' an object is made of. 'Velocity' is the component of the particle's speed acting in a specific, defined direction.
Basically the constant changing flow in a system, makes so many changes to your calculations (If I am understanding correctly so far) ??????
R's chillerman
Originally Posted by Chef
Interetsing question and an even more interesting outcome.
So the state equations seem to show the gas has no effect on the process of a 2 phase flow and therefore the corollary to this discussion so far is that the internal properties of say an evaporator can be described in fixed enthalpy values rather than a variable enthalpy.
Let me try and explain. After the TXV the value of h3 is known but as we move along the evaporator and more liquid evaporates to a gas the value of h changes and to define the properties at a new location we need to re-evaluate h from say a PH diagram.
But if we use the new equation
x=[dQ/dy*m-h4+h5]/(h4-h5)
we can now use fixed values of h namely those of the liquid line and gas line at the respective pressure. Now we can relate the fluid properties at any location with just heat input and do not need to revisit the PH diagram. The properties are defined by heat per unit length ie dQ/dy.
That would make calculations rather simpler in a 2 phase evaporator.
But this digresses from the original thread and just an interesting aside but should answer Mad's question? I think?
Chef
Originally Posted by Chef
Mad – I am not sure that putting up widget #1 is your best idea. Better to solve the process issues which will then be public and other widgets may evolve along the way.
Widget #2 is not even close to being resolved yet.
Peter – very nice to see you here and I am not sure who Boles is but he sounds interesting and we await his thoughts.
There seems to be a lot of stuff needs to be done to fully understand the bell and the consequences of messing with it can be fruitful or a failure. So far the out come as noted in my last post is to relate the properties to fixed h points and that is significant from a computational point of view.
Chef
Originally Posted by mad fridgie
Hi chef, I did have to think hard about what i was going to give, but after the last few attempts at commercialization, on other ideas, (which were somewhat easier, to prove, build and test) i have decided to cut my losses, enjoy the ride. i have been in contact with one of the big multi-national component manufactures, who showed interest, only if i could front with a full working prototype and the theorectical calculations to back other selections. They would then look at the manufacture and marketting
At this time more than i am willing and can afford to risk.
To be truthful it is not an exiting enough product/idea for venture capalists
Originally Posted by desA
I'd like to introduce the basic laws of thermodynamics, to clear up the discussion a little:
http://en.wikipedia.org/wiki/Thermodynamics
So, the moment the vapour & liquid are 'physically separated e.g. by a wall, then they can be considered in isolation, with their own states. Once separated, thermodynamic theory would then instruct you to place the new state point at its pressure/temp/enthalpy/entropy value. In some cases, the point seems allowed to 'jump' to its new position.
Perhaps we can now explore this via thermodynamic diagrams, Chef. (Very interesting thread. Making me think a fair bit... )
:)
Originally Posted by Peter_1
This will clarify
http://books.google.com/books/about/...d=5-hSAAAAMAAJ (http://books.google.com/books/about/Thermodynamics.html?id=5-hSAAAAMAAJ)
Originally Posted by Chef
OK we are both on the exact same page and 'jumping' to a new position with new properties seems to be possible but there is no precedence or rules as of yet.
The thermodynamic relations I proposed earlier seem to show this jump is supported for isobaric and isochoric processes but may only work for specific circumstances. What is the general form of the equations that allow us to jump to any part of the bell still keeping p and T constant?
So what have you found for a process at the moment that may take us forward?
Thanks
Chef
Originally Posted by Chef
So here is a PH diagram of a 4 stage drop with phase seperation. To keep it simple I have started at h2 at the outlet of the condenser and ended up at h3-4 at the inlet to the evaporator. At each location after a stage drop the phases are split into their gas and liquid forms and repositioned on the PH diagram to relevant gas or liquid line.
This is a very basic start at suggesting a process to discuss further and obvious errors include gas that has been removed at stage 1, 2 and 3 are cooled to the final evap temperature and the process should follow an isenthalpic drop but maybe we can include that at version 2 of the diagram.
Now we have the same (actually more cooling effect) cooling as a one stage drop but several gas flows at intermedite pressures that can do work. Enter the Carter Widget.
Any comments so far?
ChefAttachment 7134 (http://www.refrigeration-engineer.com/forums/attachment.php?attachmentid=7134)
Originally Posted by mad fridgie
The question then begs, when we have our various vapour streams, at different pressures (which has very little practical use in the net cooling effect) is how we can utalise the ? (being vague on purpose) to increase the pressure at the compressor suction without restricting flow in the evaporator.
What is the best possible theorectrical out come
Originally Posted by Chef
Well I presume a multi ring expander with each concentric ring sized correctly for the pressure input and flow rate to combine the flows and then use the suction provided to reduce the last section of flash gas and lower its pressure and temperature and hence get more cooling. then the final gas goes to the compressor and combines with the evap gas. Seems logical.
Originally Posted by mad fridgie
that is the problem, "it just seems logical", but somewhere in the back of mind, i feel the "Murphy effect" maybe present, the guy who trips you up at the end!
Because it is so logical, surely someone else must of been down this track?
Originally Posted by Chef
Maybe you missed my point so I will try again. We have removed gas at the 8 bar line and so this gas is no longer cooled by flashing liquid, similarly the gas at 4 and 2 bar are seperated and they also need no further cooling. In a standard TXV system all the gas is cooled to the evap temp so we have saved some energy here. The question is - is it enough to help and then we have the side streams of gas.
Got to replace the mainsail so the diagram will come later.
Chef
Originally Posted by mad fridgie
I understand, each proportion that is removed no longer requires the sensible energy removed. to the next stage.
Each stage then will have a greater amount of potential energy to be used for work. Whilst increasing the actual liquid mass flow to the evap (less total flash gas produced). Struggling in how to manufacture cheaply for small to medium systems, larger becomes much easier. (maybe this where it should be?)
Originally Posted by Chef
The savings in liquid flashing off to cool the gas is the first part. You seem to like that bit and then something like a deLaval nozzle, they can be multi ringed concentric and have nice thermo properties. Small system is a financial problem but medium would be OK. Large systems would definetly use a compander to extract the energy sucked out of the flash gas but that is known technology for decades in the cryogenic industry so not new by an means.
To get the theory of this nailed is huge - really huge so may be a while till this thread gets a final answer unless someone pops up with a neat idea!!! Still I love a challenge.
Chef
Originally Posted by desA
Ok, Chef. So you're looking for the 'jump' condition inherent within the equations - rather than simply taking for granted that the fluid 'has to' jump when split into vapour & liquid.
Let me look a little more into the equations for the 'jump' condition. Never so easy, but it should surely be there to justify the change. (I love jump conditions... :)
Originally Posted by Chef
So a small experiment is due here I feel. I pour lighter fuel on my hand and as it evaporates it gets cold, if I blow on it it gets even colder as more evaporation takes place. So you are telling me that the gas after evaporation is cold and in the time available before it disperses in the atmosphere it has time to transfer it coldness to the liquid. Yeah right I beleive that. If you wish you could provide a useful referance to support your comments.
In the PH diagram I posted there are 3 places where we propose to strip the gas away and pipe it off for its own process. The first split is at 8 bar which is 31.4C so the gas remains at that temp in its side pipe.
If we had left that gas with the rest of the refrigerant as in a standard TXV system it would need to be cooled down to -26C which is the evap temp in this case.
So we are going to need to cool that gas and the only source of 'cold' is the liquid hence my comment the liquid will cool the gas. The JT effect is not enough on its own. It is the phase transition that does the cooling.
But you say the gas cools the liquid so by dropping some gas from 8 bar to 1 bar it will cool in a process that not not only cools itself but has enough (negative) energy to also cool some of the liquid. ????
Chef
Originally Posted by mad fridgie
Actually, the liquid cools the liquid.
Liquid at saturation, "no gas/vapour" so how can the gas cool he liquid.
Part of the liquid stream absorbs energy for the remainder of the liquid stream, for the correct amount of energy to be absorbed, (to reach balance) then some of the liquid has to convert into vapour(gas). The gas/vapour is a "by product". of the process. "It is the conversion" of state
I would say that the choice of word "cool" is incorrect.
Originally Posted by mad fridgie
If the vapour does not exist, then it can not do any work. Yes it is the transformation, the new formed vapour holds the energy. No energy is transfered to the vapour after the vapour is formed, so the vapour can not cool the liquid.
Originally Posted by mad fridgie
Yes the vapour hold the energy of transformation which gives the "impression" that the vapour must of cooled the liquid. For the vapour to cool the liquid, then for heat transfer to occur the liquid has to be warmer than the vapour (vapour has to be colder than the liquid).
I supose to be factual; it is the change in pressure that cools the liquid by method of liquid to vapour transformation
Originally Posted by Chef
Good so we all agree the cooling effect comes from the latent heat of vapourisation.
So back to the point how much energy do we save by not cooling the seperated gas flows?
Originally Posted by mad fridgie
On R134a 50SCT and -30SST no sub cooling
3 takes off
30C
10C
-10C
between 9-10% extra net cooling for the same liquid mass flow
Originally Posted by Chef
I also make it 9% and we still have usefull work that the gas can do.
So next how much energy do we have in the 3 streams. Lets start with the theoretical amount and then we can reduce it by an efficiency dependant on which method id used to gain that energy.
Chef
Originally Posted by Chef
If you expand the gas at 8bar and 31C down to 4bar its temperature will end up being 26C. (Isentropic expansion)
The saturated temperature at 4 bar is 9C.
Somehow the expanded just is just not getting cold enough. It needs further cooling from the latent heat.
You have flogged this dead horse so hard even the animal rights groups are looking for you. Bury the old nag in the garden and get a new pony and call it 'Latent Heat'.
Originally Posted by mad fridgie
I think this explains all, sometimes the numbers just do not lie.
and for the humour, I like it!
Originally Posted by Chef
I have not gone quiet but at each stage I am coding it so just reset the input parameters and the answer drops out.
It takes time code and check but so far just about keeping up.
Of course I do have a distraction, well several actually as marinas are a great source of talent, sailing talent that is.
I am going for a concentric de Laval if you want to know what the widget is.
Originally Posted by mad fridgie
I may have this completly wrong, "de lavel" does the widget only do work on itself!
Originally posted by desA
I have developed some food-for-thought, for the brave, based on flow & energy principles (I trust there are no silly typing errors - please advise if so found):
http://i56.tinypic.com/8yat88.png
http://i51.tinypic.com/2vtpgfb.png
If heat is added to vapor in compressing it, then surely heat is removed from vapor in de-compressing it (stepping down it's pressure)... in which case there could be sensible heat transfer... the fully formed reduced heat content vapor in fact cooling the liquid.
How's that for beating the dead horse? :)
chillerman2006
24-08-2011, 08:11 PM
If heat is added to vapor in compressing it, then surely heat is removed from vapor in de-compressing it (stepping down it's pressure)... in which case there could be sensible heat transfer... the fully formed reduced heat content vapor in fact cooling the liquid.
How's that for beating the dead horse? :)
Argh Gary,
I see you have been to MF's Training school too, who says you cant teach an old dog new tricks :rolleyes:
You keep kicking a dog & it will bite, Basically I can either keep trying to learn or can spend all my time, snapping at the heels, easy either way !
If heat is added to vapor in compressing it, then surely heat is removed from vapor in de-compressing it (stepping down it's pressure)... in which case there could be sensible heat transfer... the fully formed reduced heat content vapor in fact cooling the liquid.
How's that for beating the dead horse? :)
If you expand the gas at 8bar and 31C down to 4bar its temperature will end up being 26C. (Isentropic expansion)
The saturated temperature at 4 bar is 9C.
Somehow the expanded just is just not getting cold enough. It needs further cooling from the latent heat.
You have flogged this dead horse so hard even the animal rights groups are looking for you. Bury the old nag in the garden and get a new pony and call it 'Latent Heat'.
mad fridgie
24-08-2011, 10:37 PM
If heat is added to vapor in compressing it, then surely heat is removed from vapor in de-compressing it (stepping down it's pressure)... in which case there could be sensible heat transfer... the fully formed reduced heat content vapor in fact cooling the liquid.
How's that for beating the dead horse? :)
I think the hourse is not just dead, it is rottern.
For your statement to be correct, the vapour has to be formed first at the high pressure then expanded, to cool the liquid. If we could imagine that this process took a larger time scale, the you would have some flash gas to start with a slightly higher pressure, as this is dropped, then it would actually cool the new vapour being produced not the liquid. But this just semantics.
gas expanding does require energy "joule thompson"
You could say a transcritical refrigeration system uses this principle.
chillerman2006
24-08-2011, 11:18 PM
Gents,
The step down in temperature you's propose from h2 through h3-1, h3-2, h3-3 to h3-4 (chefs ph chart)
How is this being achieved ???
Does your proposed vessel have multi-stages & as you remove vapour at each stage your lowering pressure each time, lowering the liquid temp ???
I am trying to follow closely & quietly, just I am getting a bit confused
Also what is the correct way to write the part in bold ???
R's chillerman
mad fridgie
24-08-2011, 11:35 PM
If you expand the gas at 8bar and 31C down to 4bar its temperature will end up being 26C. (Isentropic expansion)
The saturated temperature at 4 bar is 9C.
Somehow the expanded just is just not getting cold enough. It needs further cooling from the latent heat.
You have flogged this dead horse so hard even the animal rights groups are looking for you. Bury the old nag in the garden and get a new pony and call it 'Latent Heat'.
I think this explains all, sometimes the numbers just do not lie.
and for the humour, I like it!
mad fridgie
24-08-2011, 11:37 PM
Gents,
The step down in temperature you's propose from h2 through h3-1, h3-2, h3-3 to h3-4 (chefs ph chart)
How is this being achieved ???
Does your proposed vessel have multi-stages & as you remove vapour at each stage your lowering pressure each time, lowering the liquid temp ???
I am trying to follow closely & quietly, just I am getting a bit confused
Also what is the correct way to write the part in bold ???
R's chillerman
At this stage in the thought pattern, just thing of it as 3 vessels each with there own control.
chillerman2006
25-08-2011, 12:12 AM
This Quasistatic process really makes this whole process quite simplified
http://www.youtube.com/watch?v=WLKEVfLFau4&NR=1
Enjoy, chillerman
chillerman2006
25-08-2011, 12:23 AM
Entropy Explained
http://www.youtube.com/watch?v=PFcGiMLwjeY
chillerman2006
25-08-2011, 12:37 AM
Right I am nearly there,
I can see what happens on the ph chart when I strip away the vapour
& return to the saturated liquid curve of the bell
My calculations are
https://docs.google.com/viewer?a=v&pid=explorer&chrome=true&srcid=0B35a42p6LY0AZWYzNmFhYjctZGMwNy00YzQ5LWIxMDktN2NiYzliOGY4OThh&hl=en_GB
h3-1 = 8.0bar @ 31c
h3-2 = 4.0bar @ 10c
h3-3 = 1.9bar @ -9c
R's chillerman
chillerman2006
25-08-2011, 02:45 AM
Nice Video, Explains as all above !
http://www.youtube.com/watch?v=Xb05CaG7TsQ
R's chillerman
chillerman2006
25-08-2011, 02:48 AM
If you expand the gas at 8bar and 31C down to 4bar its temperature will end up being 26C. (Isentropic expansion)
The saturated temperature at 4 bar is 9C.
Somehow the expanded just is just not getting cold enough. It needs further cooling from the latent heat.
.
http://www.youtube.com/watch?v=iiFWoXQPOJc&NR=1
Chillerman - many thanks indeed for the synopsis of the thread as it strips away nicely the irrelevant stuff and keeps the thrust flowing well, certainly makes the whole thing much more understansable. You must have a really fast connection to get all that stuff collated. Well done.
chillerman2006
25-08-2011, 04:09 AM
If heat is added to vapor in compressing it, then surely heat is removed from vapor in de-compressing it (stepping down it's pressure)... in which case there could be sensible heat transfer... the fully formed reduced heat content vapor in fact cooling the liquid.
How's that for beating the dead horse? :)
https://rapidshare.com/files/3020151507/Boyles_s_law.gif
mad fridgie
25-08-2011, 05:17 AM
I also make it 9% and we still have usefull work that the gas can do.
So next how much energy do we have in the 3 streams. Lets start with the theoretical amount and then we can reduce it by an efficiency dependant on which method id used to gain that energy.
Chef
All gone quiet on this question.
I am going to change the question slightly, "what is the potential energy available for work in the 3 vapour streams"
A bit of assistance to get you on your way.
First stage 50C liquid to 30C converted approx 17.5% of the original liquid flow into vapour, the vapour has "h" of 413.5 Kj/kg.
Remember that the mass (amount in weight) of liquid in each stage, is reduced by the % of vapour that is being removed.
hope that gets you thinking?
I have not gone quiet but at each stage I am coding it so just reset the input parameters and the answer drops out.
It takes time code and check but so far just about keeping up.
Of course I do have a distraction, well several actually as marinas are a great source of talent, sailing talent that is.
I am going for a concentric de Laval if you want to know what the widget is.
mad fridgie
25-08-2011, 08:06 AM
I may have this completly wrong, "de lavel" does the widget only do work on itself!
MikeHolm
25-08-2011, 01:36 PM
got a pic of a "concentric de laval". It's all greek to me.
I wish I had the math for this. most of what I do is by understanding concepts and intuition.
MikeHolm
25-08-2011, 02:03 PM
No worries, found it. I thought it would be something from the dark reaches of engineering but it is pretty common.
I have developed some food-for-thought, for the brave, based on flow & energy principles (I trust there are no silly typing errors - please advise if so found):
http://i56.tinypic.com/8yat88.png
http://i51.tinypic.com/2vtpgfb.png
chillerman2006
25-08-2011, 06:34 PM
Hi DesA,
Too much bravery gets you shot, & I am not ready to become cannon fodder,
There will be less takers to this than Chef's first post ! Unless there are some mercenaries amongst the members;)
R's chillerman
chillerman2006
25-08-2011, 06:50 PM
Gents
I have found a widget type thingamegig, is this like your proposal
R's chillerman
Gents & Mr G
I have found a widget type thingamegig, is this like your proposal
R's chillerman
Nicely done. Maybe you should change your avatar to the Pink Panther.
I have developed some food-for-thought, for the brave, based on flow & energy principles (I trust there are no silly typing errors - please advise if so found):
http://i56.tinypic.com/8yat88.png
http://i51.tinypic.com/2vtpgfb.png
Somehow the url's were missing on my screen but there in the 'reply with quote'?
I will study it carefully - thanks
Des
I agree and your method was differant to mine but just as applicable and your equation 4
m1*(h2v-h1)=m2l*(h2v-h2l)
is the same as i had but you have used a differant format. Mine was an equality that needed to tend to zero to make it true and so a proof and yours is the final conditions so I like that as it becomes useable in future calculations.
Using your method we can easily see how we can go through 4 expansion and seperation processes and easily calculate the end result. I see you had to multiply both sides by -1 so the enthalpies were more understandable and I assume that is purely from a definition of W being either positive or negative but either solution is correct and so makes little differance.
I also agree gZ is small enough to be ignored and C can be treated similarly as it would be low in practical cases.
It is an elogant solution and very nicely presented and glad to see your on the case. Many thanks indeed.
Using Equ 4 I will work up a value for the 4 stage process and see what it looks like.
Chef
mad fridgie
26-08-2011, 03:08 AM
Hi Des and chef,
even though I think I understand the final equation, I am no longer up with mathmatical and scientific termonolgy.
can we please have legend!
I presume the little dots mean (square) and multiply
I can not see that the -1 calcultation, or is this just assumed and a known mathmatical method
sorry, but if i do not ask, i can not make an opinion.
The dot over the m means mass flow rate and the dot between items means multiply.
Thanks for your comments, Chef. An absolute pleasure to contribute.
MikeHolm
26-08-2011, 11:26 AM
You guys astound me. I have no idea how you find the time unless Chef is in port all the time or or he has auto-furl and powered winches and a good auto-helm.
CM, don't you need to work and is your wife starved for attention.
I can't keep up but I will try. Cheers
You guys astound me. I have no idea how you find the time unless Chef is in port all the time or or he has auto-furl and powered winches and a good auto-helm.
CM, don't you need to work and is your wife starved for attention.
I can't keep up but I will try. Cheers
Mike - Only been in a Marina 3 times in the last 20 years and no longer than a few weeks and no auto furl or power winches I lament, they are powered by cheese sandwiches and granola bars but keeps you fit I suppose. Just think about it as an office with a changing scenic view.
Chef
Here are some results condensed a bit.
If we use a standard cycle and drop from 13.3 bar down to 1 bar with a standard TXV and assume 1 for the mass flow we get a cooling effect of 111.6 Kj
If we go through a 4 stage let down as shown on the PH diagram posted earlier and useing the formulae from DesA then we have a cooling effect of 120.6 Kj
Each of the 4 stages was anaylsed and the results added together.
This extra cooling effect comes from the fact the gas is seperated and does not require any further cooling. So now we have 3 streams of seperated gas at 8, 4 and 2 bar and these streams will contain the missing energy so there is 9Kj available if we can use the gas efficiently. Even if we only get 50% usage then the total energy added to the cycle will be 13.5Kj
Chef
Very interesting results & feedback, Chef. Thank you.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.