View Full Version : Hydraulic Lock/Exploding Pipework



chillerman2006
11-08-2011, 12:17 AM
Everyone who is not aware of Hydraulic Lock - should be

from the pics you can see this could have caused some-one serious harm

Magoo
11-08-2011, 01:38 AM
A potential/ constant problem in industrial systems with sub cooled liquid lines. The power of warming liquid will split wide open a steel walled pipe.

chillerman2006
11-08-2011, 01:47 PM
the cause behind this rupture was a fault with the expansion valve & a mistake by the customer

the circuit pumped down creating a fault alarm on the bms, so the customer decided as he had an a/c engineer attending site to carry out maintenance he would be able to rectify the problem more cheaply than my own company

the liquid line valve was closed by the engineer and was not re-opened

leaving subcooled liquid trapped between the two valves

within an hour of the engineer leaving site the trapped liquid's temperature rose & boom

It made such a bang that it was heard by the customer from his office

who needless to say learned very quickly - horses for courses
:D:D:D

Magoo
12-08-2011, 05:19 AM
Hi Chillerman 2006,
I think your client has just become a captive listener, and afreind for life.

chillerman2006
12-08-2011, 09:55 AM
Hi Chillerman 2006,
I think your client has just become a captive listener, and afreind for life.

Hi Magoo

your not wrong there mate

install monkey
26-08-2011, 11:37 PM
horses for courses! haha not in ur case mate!!!haha

the cause behind this rupture was a fault with the expansion valve & a mistake by the customer

the circuit pumped down creating a fault alarm on the bms, so the customer decided as he had an a/c engineer attending site to carry out maintenance he would be able to rectify the problem more cheaply than my own company

the liquid line valve was closed by the engineer and was not re-opened

leaving subcooled liquid trapped between the two valves

within an hour of the engineer leaving site the trapped liquid's temperature rose & boom

It made such a bang that it was heard by the customer from his office

who needless to say learned very quickly - horses for courses
:D:D:D

chillerman2006
29-08-2011, 08:17 AM
not in ur case mate

You've obviously been miss-informed, I have had the site now for past 6 years & no-one is allowed near the plant on the roof anymore, there are 12 units totalling just under 5mw of cooling & even though they do their own coil cleaning, I have to be there ! cctv has also been installed ! It is as I said 'horses for courses' you may run rings around me doing a/c installs but your still be at the starting gate when I have finished on this sort of kit. About time we see some of your work pics annit or even a video, explaining how they work, I may even learn something !

install monkey
29-08-2011, 10:15 AM
col-i was highlighting the choice of of word-horses- as you say chillers yep-blackmans magic-i can work on em ,change compressors and **** but as for stripdowns,stuff that.
i did an install on sat did 4 flares and didnt **** up haha-will get some pics up-not of me mrs though too many pink pixels haha
You've obviously been miss-informed, I have had the site now for past 6 years & no-one is allowed near the plant on the roof anymore, there are 12 units totalling just under 5mw of cooling & even though they do their own coil cleaning, I have to be there ! cctv has also been installed ! It is as I said 'horses for courses' you may run rings around me doing a/c installs but your still be at the starting gate when I have finished on this sort of kit. About time we see some of your work pics annit or even a video, explaining how they work, I may even learn something !

chillerman2006
29-08-2011, 10:22 AM
col-i was highlighting the choice of of word-horses- as you say chillers yep-blackmans magic-i can work on em ,change compressors and **** but as for stripdowns,stuff that.
i did an install on sat did 4 flares and didnt **** up haha-will get some pics up-not of me mrs though too many pink pixels haha

Oh ! ok was looking at it upside down :)

desA
29-08-2011, 11:47 AM
The piping schedule seems pretty thin, I must say.

If the correct wall thickness is used, then the piping should have a burst pressure of around 70 bar(g), unless fully annealed. Even then, I'd expect an expanding liquid to be less than this. Would be very interesting to do the calculations on the evolved pressure.

Interesting.

chillerman2006
29-08-2011, 11:59 AM
The piping schedule seems pretty thin, I must say.

If the correct wall thickness is used, then the piping should have a burst pressure of around 70 bar(g), unless fully annealed. Even then, I'd expect an expanding liquid to be less than this. Would be very interesting to do the calculations on the evolved pressure.

Interesting.

Phew ! way over my head mate, I am just glad it went pop before I got there to sort it out, otherwise I could have been leaning over that checking out the valve :eek: when i am there next will see if there is still some of the pipe on site & get it shipped out to you

install monkey
29-08-2011, 12:02 PM
doubt it the scrap monkeys will have had it off!!!!

chillerman2006
29-08-2011, 01:27 PM
doubt it the scrap monkeys will have had it off!!!!

possibly but am sure I just slid it under the unit when I replaced it, & my other tubes still there from when I carried out the mods, just stuck a small peice of tube with an nrv around the solenoid valve to all 24 circuits £$£$ ca-ching ! ;) joys of cctv

install monkey
29-08-2011, 01:36 PM
we had to rip out 10x 3m lengths of 800a bus bar track each section weighed 70kg. full of copper bar and about 10kg of plastic/aluminium.we stripped it out and stacked it all up. the customers electrical contractors weighd it in,the project manager went apesh*t accusing us of having it off,luckily theres more cameras in a debenhams loading bay than stock so my arse was covered!! yay the joys of cctv
possibly but am sure I just slid it under the unit when I replaced it, & my other tubes still there from when I carried out the mods, just stuck a small peice of tube with an nrv around the solenoid valve to all 24 circuits £$£$ ca-ching ! ;) joys of cctv