View Full Version : Package units commissioning



zenen
04-08-2011, 12:27 PM
Dear fellow experts,

I have a package unit with downflown configuration, (raised floor 600mm), connected with an external condenser unit.

Refrigerant piping is 1, 3/8 & 7/8 no longer than 10meters. Refrigerant charge is around 24kg.

Design pressure test is at 24bar.

What pressure test would you advice that I use. 30bar or 40bar? and how long...lets say for 24hrs?

thanks,

Z

james10
04-08-2011, 01:35 PM
no more than 24bar

Magoo
05-08-2011, 02:46 AM
1.5 times the normal working pressure and below any safety releif valves, for 24 hours.