View Full Version : denco ccu trouble



aliman
03-08-2011, 01:32 PM
Hi,can anyone help I have several ccu's with humidifier faults arrived on site found existing bottles scaled up changed all tried to reset faults on trend excite front end. now 4 bottles dont even fill and the others are working but still show hum faults changed fill valves,checked water to unit ok.any help much obliged.model. D94. FVH and D54AVH.

Denco Technical
04-08-2011, 01:00 PM
I would suspect you have a fault code on the hum board.

Can you confirm what lights are flashing and the sequence.

Thanks

aliman
16-08-2011, 10:11 AM
Hello rob,thanks for reply,on hum boards I have a constant green led and a red led flashing 7 and then 8 times continuosly.cheers, ali.

Denco Technical
22-08-2011, 09:24 AM
Hello rob,thanks for reply,on hum boards I have a constant green led and a red led flashing 7 and then 8 times continuosly.cheers, ali.

Okay, it sounds like the hum board is in fault, drop me a email and i will send you the O&M for the hum board as its too big to attach here.

rob.woodworth@geagroup.com

Denco Technical
22-08-2011, 03:35 PM
email sent.