View Full Version : Hitachi RAS20-FSN (VRF) Advice/Manual needed



james10
26-07-2011, 03:08 PM
I have just picked up a site with the above units on and one of them is giving an error 51 message, i have never worked on these units before so any help or advice would be greatly appreciated.
Thanks in advance
James

joe-ice
26-07-2011, 04:28 PM
book says its an abnormality of current sensor for the inverter compressor.not reading current when compressor should be running or faulty pcb 2 board

james10
27-07-2011, 01:24 PM
Thanks Joe Turned out to be the Compressor PCB

fordjarini
28-08-2011, 12:57 PM
51 = Abnormality of inverter current sensor. Failure of sensor or inverter PCB
Alarm codes : http://www.hitachiaircon.com/argws/html/helpingyou/en/AlarmCodes.pdf

HITACHI : http://www.hitachiaircon.com