Which brand of controllers from the shelf can control these valves?
Carel and Dixell apparently can't.
Guess Eliwell can't neither.
Any suggestions?
We have a blown up PCB on a chiller - complete standstill now - and a new PCB is not ready available.
This is very urgent. Client has to rent now a chiller which will cost +/- 16.000 €/week (!!) and +/- 12.000 €(!!) to connect it.
Haven't found a Siemens controller neither.
Yuri B.
25-07-2011, 05:29 PM
The EEVs themselvs cannot be replaced with other brand for which there is a controller?
Peter_1
25-07-2011, 05:43 PM
Searched too far, Siemens has their own Polycool controller. I will ask tomorrow morning where those are available.
http://www.siemens.cz/siemjetstorage/files/60310_023$RWR462$1$.10$en.pdf
Josip
25-07-2011, 05:53 PM
Hi, Peter_1 :)
Which brand of controllers from the shelf can control these valves?
Carel and Dixell apparently can't.
Guess Eliwell can't neither.
Any suggestions?
We have a blown up PCB on a chiller - complete standstill now - and a new PCB is not ready available.
This is very urgent. Client has to rent now a chiller which will cost +/- 16.000 €/week (!!) and +/- 12.000 €(!!) to connect it.
Haven't found a Siemens controller neither.
Not sure, but maybe you can install new EEV Valve complete with belonging controller from Danfoss, Honeywell, Carel whatever is available on stock.
http://catalog.carelusa.com/viewitems/electronic-expansion-valves-3/electronic-expansion-valves-2
http://www.google.com/url?sa=t&source=web&cd=4&ved=0CDEQFjAD&url=http%3A%2F%2Fwww.honeywell-cooling.com%2Fpdfs%2Fproducts%2FElectronic_Controls%2F2_Electronic_Expansion_Valves%2F1_EEV2%2FDB%2F en%2FKAT-EEV-001%2520EN0H-1945GE23%2520R0310.pdf&rct=j&q=EEV%20Valve%20&ei=RZwtTpb9D8-Uswac75D3Dw&usg=AFQjCNEarbRk-A_P1Kfl1sDUFbyuPZfV9g&sig2=6nVao47u981KVjou947g2Q&cad=rja
http://www.danfoss.com/BusinessAreas/RefrigerationAndAirConditioning/Products/Group/RA/Electronically-Operated-Valves/ETS-Expansion-Valves-for-Fluorinated-Refrigerants/f29a737b-3fc2-402b-b012-55beafca078f.html
Hope this will give you some idea ... sorry cannot help more.
Best regards, Josip :)
Peter_1
25-07-2011, 08:47 PM
That's the last option Josip because this is a much bigger and more expensive job then. If we should change, then I should go for Carel because we used those already in the past. Danfoss is another option.
The controllers of Siemens are costing +/- 350 €, just hoping now they're ready available.