View Full Version : problem with toshiba ras-10skv-e
saskld
25-07-2011, 04:08 PM
Hi,
my air conditioner stopping cooling my room.
Led green and yellow are on.
Fault code 1F.
If I set temperature to 25C or 18C the fan speed of compressor running same speed.
Room temperature 28C without cooling.
Air conditioner is 3 years old.
What is there wrong on my air conditioner?
martinw58
25-07-2011, 08:19 PM
hope this helps pos faulty comp or contactor
More specific codes may be obtained, while in the fault mode through the wireless controller
1. Press CHK to enter service mode
2. Navigate through TIMER
buttons until all LEDs flash, accompanied by the internal buzzer – compare the displayed code with the table below
3. Press CLR button to clear the existing fault code (controller displays 7F)
Press ON/OFF button to exit service mode.
Initial code/display
Code
Description
01
0C
TA sensor open or short circuit
0d
TC sensor open or short circuit
11
Indoor fan motor problem
12
Indoor PCB problem
01
04
Indoor to outdoor communication (includes compressor thermostat)
05
Indoor to outdoor communication
02
14
Inverter low voltage or short circuit protection
16
Compressor position circuit
17
Compressor current detected during off-cycle
18
TE or TS sensor open or short circuit
19
Td sensor open or short circuit
1A
Outdoor fan motor problem
1b
TE sensor fault
1C
Compressor drive circuit
03
07
Indoor to outdoor communication (includes compressor thermostat)
08
Indoor heat exchanger changes temperature – but in wrong direction
1d
Compressor locked rotor current protection
1E
Compressor - high discharge temperature
1F
Compressor current remains too high – after current release