View Full Version : Dx no cold return



devlin maguire
14-07-2011, 11:38 AM
New compressor 3 months back MManeurop performer, R22 45KW HS 17bar LS 5 bar cutting out on gas discharge temp sensor SC spot on at 10K as per Airedales recommendation however suction line is warm, TEV is frosting, almost, general opinion is a failed TEV /restriction, any comments any one, I have mentioned this in another thred but the heading may be misleading as it was regards another issue, existing is TEX12 with a 3 orifice.
Devlin