View Full Version : ASHA12LGC outdoor unit do not work



d00b
03-07-2011, 09:59 AM
Dear Sir,
I have Fujitsu General split system ASHA12LGC.
LED indicators shows serial reverse signal error at operation start up
Indoor unit works correctly
Terminals outdoor unit and indoor unit are connected correctly.
I switch on split system and check voltage in the outdoor unit
Voltage in the plug socket is 203 - 213 V.
Voltage between "earth" terminal and "L" is 28 V
"earth" terminal and "N" is 28 V
"earth" terminal and "3" is 28 V
Voltage between "N" terminal and "L" is 0 V
"N" terminal and "3" is 0 V
"L" terminal and "3" is 0 V
Please, send me repair manual for that model of split system
or give any idea to solve this problem

stufus
03-07-2011, 10:56 AM
Try Google !! Its amazing what you can find in a few seconds.
http://www.redtechnologyshop.com/public/RedTechnologyShop/Prodotti/2487/Service%20Manual.pdf
Cheers
Stu

P.S. Check the inline fuses from the terminal blocks

install monkey
03-07-2011, 05:20 PM
after the 3 min start delay u should have 240v on L 240v between L and N and 3 is a pulsed signal.
check the outdoor isolator and check your getting these voltages off the indoor unit,if not then your power relay is the only thing preventing power on the L terminal

d00b
05-07-2011, 06:11 AM
Thank you stufus I downloaded manual.
The outdoor unit fuse not damaged.
Dear install monkey
really power relay preventing power on the L terminal
What voltage should come from controller to the power relay coil?
what you mean when said "check the outdoor isolator"?
May I turn on outdoor unit from plug socket without indoor unit?
Thank for answer.