03-07-2011, 04:19 AM
Guys I'm having a problem with the standby on this unit. When I plug it into 1 phase the overload switch trips when the compressor engages. The compressor turns freely by hand so I don't think that its locked up. What could be causing this? I'm stumped.

Edvin
03-07-2011, 08:15 AM
If I remember right the overload can be adjusted(you can adjust curent at witch it disengages). You could try to run the motor alone without compressor(remove the belt)

charlie patt
03-07-2011, 07:45 PM
ive had the timer locked out so the clutch is engaged before the electric motor at full speed pull wire of comp and sea what it does

lextronman
03-07-2011, 11:25 PM
Tweaked the overload switch and it seems to be working now. Will overvoltage on the overload shorten the life of the micro? Thanks for the help.

cadwaladr
04-07-2011, 01:39 PM
how long is the power cord you are using and what guage is it because its a common problem people make with single phase units.

MRW
01-08-2011, 04:26 AM
What is the overload set for? Can u check the amp draw when running on standby at the
Standby cable?

chillerman2006
07-08-2011, 01:15 PM
Pitted contacts in the contactor is another

check for volt drop across the contactor