is it possible to convert the existing glycol evaporator into r-22 evaporator?
my concern is, glycol type has no distributor and txv, is it fine to change the inlet and put a distributor and txv?

Sandro Baptista
29-06-2011, 01:56 PM
If it's for pump system it will work well, still it's not optimized for that 2 phase flow.

install monkey
29-06-2011, 10:41 PM
am i understanding that u want to drain your wet, cooler and pipe r22 through the cooler to use it as an evaporator.
system pressure would be a concern,what about the auto air vent/drain point, this sounds like a disaster in the making.
i recommend getting a new evap coil designed for refrigerant with distributors and expansion valve. and u get chance to recycle the old coil/scrap yard

weng-alms
30-06-2011, 02:37 AM
hi guys,
i am condemning it, we will supply new accu for r 22 and trying to figure out if we could utilize the existing glycol evap'r, kinda installing a distributor & txv, application temperature is +8 deg c.
what do you think guys?

Sandro Baptista
30-06-2011, 11:24 AM
How much would cost you a new evaporator coil for R22 DX?

weng-alms
01-07-2011, 03:40 AM
hi SB,

that's my problem, it is clients call. anyway here in Philippines that would cost almost 2M (importation), unit cooler alone.
for them it would be a waste of money. and besides it will be scrapped.
on the other side conversion would cause a lot of trouble and inefficiency, i will take your point, it will be a disaster if we go on conversion.

thanks a lot SB.

Sandro Baptista
01-07-2011, 09:04 AM
2M?? What's the coin? Tell me in American dollars...or Euros.

weng-alms
04-07-2011, 08:43 AM
PhP, that's 30000 usd.

Sandro Baptista
04-07-2011, 12:48 PM
PhP, that's 30000 usd.

Each evaporator coil?? A lot of expensive. Now I understand you try to retrofit the coils...

weng-alms
05-07-2011, 03:53 AM
yes, all charges includes, tax & mobilization. :)