Hi,
i want to check and maybe add refrigerant to a compressor (Aspera NEK 6187Z, 1Hp - R134A). this compressor is used to maintain a temperature of 18-20 degrees celsius to a small room.
the problem is that i don't know which must be the pressure in the low side and how i can find this value.


thank you.

jayryu
16-06-2011, 02:06 PM
What kind of system it is? Captube or TXV? Low side pressure changes according to box temperature in Captube system and evaporator outlet temp in TXV system. You have to refer to PT chart of R134a.

Brian_UK
16-06-2011, 10:42 PM
the problem is that i don't know which must be the pressure in the low side and how i can find this value.
Then perhaps you should contact a technician who can do it for you.

jjprotos
20-06-2011, 08:13 AM
It is captube.

jayryu
20-06-2011, 04:59 PM
low side pressure to be around 40 psig at 18~20'C box temp.

jjprotos
21-06-2011, 12:32 PM