View Full Version : compressor overheat failure



waleed
14-06-2011, 11:21 AM
I have a mitsubishi reefer system that runs for five minutes then stops due to alarm code 413,.Any suggestions on how to solve this problem or what may be causing this?

pacey
15-06-2011, 09:10 PM
have u checked the gas charge of the unit as it could be low causing the unit to over heat and tripp due to the lack of suction temp or the condensor is blocked or unit is overcharged or the sensor is faulty take more reading of the suction temp discharge temp and compressor temp also running ampthis would help to sole the problem i hope