hi all,

can anyone assist me on trying to fault find a p30 error code.

i have a vrf with a system controller which has one group i gather making it have 1 master 4 sub units.

i have not really worked on sanyo vrf.

should i be getting o volts on the transmission line, i seem to be but getting 17vdc on the remote control line.

any help would be appreciated

cheers

install monkey
07-06-2011, 07:08 PM
P30 Indoor unit fault, System controller detected fault on sub indoor unit

moondawn
07-06-2011, 07:13 PM
hi install monkey, not familiar with these sanyo vrf units. how can i tell what the fault is with the unit and also pinpoint which unit has the fault.

install monkey
07-06-2011, 07:29 PM
check indoor unit for the one not operating and check the hi limit condensate float-pull the drain plug to see if it restarts

moondawn
07-06-2011, 07:34 PM
i went round the ducted fan coils to see if one was not working and the rest was but did not seem to find the problem unit. i also had a h6 error on this system which i know is compressor low pressure activation.

install monkey
07-06-2011, 07:43 PM
u have mail!

moondawn
07-06-2011, 08:12 PM
cheers mate . would you believe it mentions nothing for p30 error in there, thank you for your efforts

install monkey
07-06-2011, 08:20 PM
tony duffy-is mr sanyo!!

moondawn
07-06-2011, 08:34 PM
yeah just seen a post saying he back online so hopefully he can assist. thanks installmonkey

techguy
08-06-2011, 03:51 PM
HI Guys,

P30 is a fault on an Indoor unit or group of indoor units which has no remote controller installed on it.
If you have identified the group you must connect a controller to the master indoor unit in the group to identify the fault. You can borrow one from another area if you don't carry a service remote.
Once connected and switched on the controller should display the actual fault. This time of year most likely P10 condensate pump fault . But could be anything.

I left my SANYO mail addy on here last time use this to contact me if you need too

Regards
T

moondawn
09-06-2011, 08:07 PM
many thanks tony i have the controller on order from climate centre.