View Full Version : Daikin outdoor main supply RCCB triped



sachin230
07-06-2011, 07:18 AM
I have Daikin 30HP, VRV III system with 13 indoor units. This is New installation before two year

Outdoor model: RXYQ18PY16 & RXYQ12PY16, Indoor Model:FXFQ100PVE

Today outdoor main supply RCCB triped due to that all indoor units corded remote shows "U4"error.

RCCB specification : Legrand make RCCB specification :415v,C63 Icu -10000ka,10KA & another attached 0.1A,100mA

please suggest, which is the possible reasons for outdoor Main supply RCCB triping.

your feedback much appreciated

Magoo
08-06-2011, 12:47 AM
Either RCD breaker is faulty, or you have earth leakage problem. First have RCD tested and varify accuracy.

JoeAT50A
08-06-2011, 07:58 AM
Two outdoor unit for one breaker, are you sure diakin recommend 63Amp Type C? If so, you have some earth leakage.

sachin230
09-06-2011, 10:57 AM
Thanks for reply
How to rectify the earth leakage problem ?
I observed outdoor RCCB tripped in rainy season. why?

install monkey
09-06-2011, 06:41 PM
daikin recommend 2a power supply for each outdoor unit.
check for water in yor isolator,reset breaker and prove 415v at each condenser.check internal fuses,test insulation of all 6 compressors,prove operation of each compressor,test inverter circuits