06-06-2011, 07:18 AM
Hi all,
I have a PFH050 chiller with two CE050 compressors running with R12.
I lost oil in 1st compressor. I put new oil and I started. It run OK.
When a compressor run and the other one is stating, it trips (the 2nd started) by high suction temp.
Do you know if the suction valves are butterfly or other type? The unit is very old I don’t want to touch these valves before I know what kind they are?
I have a feeling that the unit need refrigerant or the suction valves are not open enough.
When evaporator pressure is 45PSIG, the pressure in suction elbow is 38PSIG.
When compressor trips by high suction temperature, suction is hot and bellow suction valve is cold!!!
What is your opinion?
Regards,
CV