kkwong0
31-05-2011, 03:35 PM
Hi all,
I'm looking for a 2 HP, and a local vendor propose a 2-1/4 horse Bristol H23B30QDBE as shown in his spec below. But when I doublechecked the spec from Bristol (below as well), the compressor has a BTUH of 30100. If I got it rite, 30100 is approx 11.8 HP or 8.8 kilowatts. I could have probably missed out something here....
Another question:
@45/100 - @45/130: Do these values on the Bristol catalogue refer to the compressor capacity at the SST of 45 degree and SCT at 100 or 130 degree?
Please advice, thks
Bristol compressor
Model: H23B30QDBE
Vendors' spec:
===========
CV: 2-1/4
Capacity in Watts at +5°C: 6,666
Capacity in Watts at 0°C: 5,326
Capacity in Watts at -5°C: 4,147
Capacity in Watts at -10°C: 3,122
Spec below is from Bristol catalogue:
===========================
@45/130
---------
Capacity BTU/H: 30100
Capacity WATTS: 8832
Motor input watts: 3100
ERR/COP BTU/WH: 9.7
ERR/COP W/W: 2.8
@45/100
---------
Capacity BTU/H: 37626
Motor input watts: 2503
EER BTU/WH: 15.0
I'm looking for a 2 HP, and a local vendor propose a 2-1/4 horse Bristol H23B30QDBE as shown in his spec below. But when I doublechecked the spec from Bristol (below as well), the compressor has a BTUH of 30100. If I got it rite, 30100 is approx 11.8 HP or 8.8 kilowatts. I could have probably missed out something here....
Another question:
@45/100 - @45/130: Do these values on the Bristol catalogue refer to the compressor capacity at the SST of 45 degree and SCT at 100 or 130 degree?
Please advice, thks
Bristol compressor
Model: H23B30QDBE
Vendors' spec:
===========
CV: 2-1/4
Capacity in Watts at +5°C: 6,666
Capacity in Watts at 0°C: 5,326
Capacity in Watts at -5°C: 4,147
Capacity in Watts at -10°C: 3,122
Spec below is from Bristol catalogue:
===========================
@45/130
---------
Capacity BTU/H: 30100
Capacity WATTS: 8832
Motor input watts: 3100
ERR/COP BTU/WH: 9.7
ERR/COP W/W: 2.8
@45/100
---------
Capacity BTU/H: 37626
Motor input watts: 2503
EER BTU/WH: 15.0