View Full Version : broblem with TK SMX II SR μPIV CRAZY .......



tspgr
27-05-2011, 08:05 AM
Hello to all
i have a broblem with a tk smx ii μpiv with electric.
The unit in disel mode works all fine.
But on electric when it is on continuous start directly with the open off the on off switch works for five min. With no control off temp (cool only) and then gives alarm 16
when its on cycle centry start with the wright order ( buser timer cool light condactor on) works for 1 min and then alarm 10 ....

I have replace to check :

Micro - pc board - fase module
it still gives my same think my brain is cooked


please help
thanks in advance
mike

gravy258
27-05-2011, 10:53 AM
is the oil pressure switch going to ground with engine off
are there two HP switches on the compressor
is the electric motor phase correct, check direction of rotation

clivemtk
27-05-2011, 09:43 PM
code 10 -high pressure circuit code16 - manual start not completed

gravy258
29-05-2011, 06:25 AM
code 10 -high pressure circuit code16 - manual start not completed

i think we get that part...

tspgr
30-05-2011, 03:01 PM
thanks a lot for the answers but the problem was that i did not have the return of 7EH to the pin of the micro broken wiring ......
i find it repair it all working just fine now


:)