PDA

View Full Version : Condensing temp of refrigerant



anup
02-10-2005, 08:23 AM
In Air Source Heat Pump, where the condensing medium is water, to get hot water at 60 deg. C., what should be the condensing temp of refrigerant?

Horatiu
02-10-2005, 05:53 PM
Hello Anup. If you want to get hot water at 60 deg. C the condensing temperature of refrigerant must be bigger then the temperature of water. 64-66 deg. C should do it.
Best wishes.:)

botrous
02-10-2005, 10:18 PM
Hi Anup , in any heat exchanger , to heat a substance at least you need the tempreture of the heating substance to be the desired tempreture of the heated substance + .

Like if you want to heat water from 10*C to 20*C , at least you need a heat source of 21*C .
The capacity should also be calculated , I mean you can't heat 10 Kg of water from 10 to 20*C with 5Kg of water at 21*C .

The same principle applies to your question

Lc_shi
04-10-2005, 06:51 AM
Hi anup
it will depend on your heat exchanger design. Usullay 3~5K is the lower limit. Too small temp diff will cause bigger size heat exchanger and increase cost.

rgds
LC

anup
04-10-2005, 03:14 PM
Hi, How to calculate over all heat transfer co-efficient for a eveporator and how does it corelated with tube thermal conductivity ?