View Full Version : compressor for coldroom
ah fai
25-05-2011, 03:49 PM
halo, everybody, another question about which type for bitzer compressor suitable for my coldroom and the total cooling capacity calculation...thanks
sizing - length 40ft
- wide 25ft
- high 20ft
temp 0 ~ -5 degree c
Josip
25-05-2011, 09:47 PM
Hi, ah fai :)
halo, everybody, another question about which type for bitzer compressor suitable for my coldroom and the total cooling capacity calculation...thanks
sizing - length 40ft
- wide 25ft
- high 20ft
temp 0 ~ -5 degree c
What kind of goods and how much you want to keep within your cold room,
or you plan to keep it empty?;)
Best regards, Josip :)
ah fai
31-05-2011, 07:47 AM
around 20ton of fruit & vegetable
tonyelian
05-06-2011, 01:38 PM
hi
you need 48 kw compressor 6j-22.2y-40p hope it help
Peter_1
06-06-2011, 07:29 AM
If you want cooling capacities, then you have to give us all the info to calculate it. It will vary from 5 till 100 kW and all answers will be correct.
w.l.ong
25-09-2011, 05:46 PM
hi,
Heat load calculation, need lots INPUT, as it will loading your compressor.
without this Input you are lost, As Peter_1 said...5 to 100KW...hahahah
don't forget the product SH (Specific Heat) or (latern heat) is also playing a big rules.
I trust my software.
w.l.ong
Sumit
27-09-2011, 01:36 PM
Hi,
As others said , you should give us the all details of your cold room like u said 20 tones of fruits and vegetables.Please give us other details like lighting system, on which floor it is , roof is covered or not ; everything which are the source of heat generation should be considered.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.