PDA

View Full Version : UNISAB III Voltages



smartemea1
19-05-2011, 10:26 AM
Hi All,
I am currently faced with a voltage issue on a UNISAB III controller fitted to a Frick screw compressor. The Sabroe wiring diagram, (4849-961), indicate a voltage input onto the Power Supply terminal X20. The output to the unload solenoid from Digital Output terminal X8 is marked as "Internal Supply" but is measured as the same voltage. I am having a Neutral issue and was wondering if the supply voltage is being "isolated" from the voltage used for the unload solenoid via an internal transformer, which is not indicated on the drawing. Could this be the source of a potential Neutral issue?

Grizzly
22-05-2011, 09:29 AM
Hi Smartemea1

The internal supply voltages (terminal block X8) are dictated by the voltage input you supply to X20.
Hence you are getting the same voltages as input.

You say you have a neutral issue? Could you elaborate a little more?

Grizzly