PDA

View Full Version : GAH rapier fans not working



fridgetrouble
18-05-2011, 03:35 PM
Should change my name to fridge virgin.
Have a GAH rapier, set at 2 degres. the unit is cooling down both on road only and on standby to 10/11 degres and then cutting off.
Fans on top not working/turning. Any idea ?
many thanks

transport guy
19-05-2011, 07:24 AM
Fans not working at all on the condenser on the roof? If not fuses usally blown 15 amp in a metal box in condenser/or in inline fuse holders

cadwaladr
20-05-2011, 12:11 AM
yep check the fuses,the motors are more than likely u/s,on the later units they are thru a pressure switch so check that as well fuses first.

vehikool
25-05-2011, 06:42 PM
Hi also check the condenser fan relays as they can burn out (this is after you have checked the fans for being siezed or badly worn, check amp draw on each fan assy) make sure you fit the correct relays some GAH relays have a double 87 terminal. Also contact GAH for a wiring diagram, they are quite helpful.
hope this helps
regards
Tom

transport guy
26-05-2011, 07:27 PM
where abouts in the uk are u,if your close ill fix it for a case of beer, 9 times out of 10 fuses blown after winter due to design fault.