View Full Version : Advice for dryer operation
paul441
03-05-2011, 07:52 PM
Hi guys
After some advice on dryer operation , being working on dryers for few months as new to refrigeration game. anyway what does compressor indicate when its pumping but its very hot, have a dryer that seems to be running at normal dp fan coming in etc but comp very hot. gas r410a cheers
chemi-cool
03-05-2011, 08:14 PM
Its the first time I hear about 410 being used in dryers, is that what the manufacturer originally used?
For your question, hot compressor is lack of cooling, means, it short of returning gas. Could be undercharged, blocked drier or whatever, leak in the system.
install monkey
03-05-2011, 09:51 PM
is the condenser coil clean-ie between the fins. a clean condenser can lower head pressure,reduce compressor temps and improve performance
Magoo
03-05-2011, 10:51 PM
Usually driers have a hot gas injection valve, if over feeding can cause the overheating problem.
glenn1340
04-05-2011, 04:45 PM
i`ve not seen any driers with r410. As chem-cool says it could be low on gas, there again maybe condensor problems. Dryers can be strange things, you`d think being low on gas would cause the DP to go up. it will when the refrigerant gets too low but until that piont is reached it could even freeze up, then as more refrigerant is lost the DP wil go up.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.