View Full Version : Daikin unit changing from cooling to heating itself..???? HELP
Ash Khan
05-04-2011, 11:08 AM
Hi All,
We have 2 cassettes & 1 outdoor Daikin unit in one of our lab, we keep this unit on cooling all the time but it’s changing itself to heating.
We have one wall mounted control also with master digital control.
Did anyone can help me to find out what is the reason?????
Many Thanks
Ash
croc1774
05-04-2011, 12:01 PM
Check the controller i would bet its been changed to auto mode and not just cooling mode.
frank
05-04-2011, 04:12 PM
It would be helpful to have some model numbers and further details of the digital master controller
install monkey
05-04-2011, 08:12 PM
weak coil on the reversing valve can cause the system to start heating without warning with no fault codes.
is the 7 day timer programmed beacause this can either start up as last set or start up at a programmed setpoint and mode!
JoeAT50A
06-04-2011, 08:06 AM
4 way valve is activated somehow, may be due to Auto-mode, Master should control mode and use lock function so called prohibit function to lock the mode. How is your ambient temperature? Some outdoor temperature will trigger the heating mode.
Ash Khan
03-06-2011, 08:14 AM
Dear All,
Sorry about the late reply. I was off for holidays…J
I had a look in the master control and the system was on auto change over, so what I done disable all the auto change over setting to cooling only….Problem Solved.
You guys are GREAT!!!!!!!!!
Thanks for all your support and help..
Ash
JoeAT50A
03-06-2011, 09:56 AM
Dear All,
Sorry about the late reply. I was off for holidays…J
Ash
Congrat Ash, not that too late .... just two months.
Hope you had solved this issue two months ago, not recently right?
Ash Khan
03-06-2011, 10:18 AM
Thanks Joe,
LOL …..Yes I solved the issue when I received your reply on 06/04/2011 and got busy at work sorry once again and thanks once again for your help.
How’s Air Con work/business in Singapore?
Best Regards
Ash
JoeAT50A
03-06-2011, 10:27 AM
Not at all Ash, just kidding.
In Singapore air-con business is good due to hot tropical weather.
In fact need not to thanks me man, I have no idea on Heat pump, we only use cooling only.
Have a good day!
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.