this unit i am working on works fine problem is the red light flashes after its been running for 30 minutes,the code p22 is present no active alarm my understanding is 22 code is condensor fan not working but its operating fine cuts in and out no prob? am i missing something.:confused:

clivemtk
04-04-2011, 09:18 PM
open circuit condenser fan getting warm after 30mins

cadwaladr
04-04-2011, 09:59 PM
i dont think so because it works fine it only runs [the fan that is ]for 5 minutes until pressure drop but it could be that,will see it again tomorrow and will postl

charlie patt
05-04-2011, 09:05 PM
if fan pulling to many amps will bring fault up or corrioson on pin terminals to brain

cadwaladr
05-04-2011, 10:31 PM
thanks for info,my guess is the latter will let you know.

clivemtk
07-04-2011, 07:51 PM
does cadwaldr not say it is bringing up code22

vehikool
14-04-2011, 07:49 PM
Hi Cadadwaldr one of the problems with the Carrier fan motors are that the brushes tend to stick in the motor, try removing the fan motor unscrew the black brush retaining caps, pull on the brush spring end plate and the brushes should slide in and out freely, if they do not fit a new set of brushes and brush holders.
suggest this is worth a try.
hope this helps
Tommycool

clivemtk
18-04-2011, 09:02 PM
hi cad how did u go on with fault

cadwaladr
18-04-2011, 09:16 PM
its gone off the hot burner for the moment cos it will only pull -11 c the insulation looks like its not up to it,the fan motor works as it should?.