PDA

View Full Version : Maxima Defrost Problem



bellg
24-03-2011, 01:35 PM
Hi, I have a Maxima 1200 that I cant get to defost.
I suspect the defrost thermostat switches but am not sure.Beside the two DT's there is another small switch with 2 white wires. Is this related to defrost. How are these checked out.?

djbe
24-03-2011, 07:16 PM
Try linking the DT's out. If it goes on manual defrost then you know that is the problem.

long server
24-03-2011, 07:16 PM
The small klixon will be for the suction bypass if it's a solid state controller and not micro - favoraite on these is 3 way valve passing if it terminates when receiver is front seated that's wat it will be -if it's energised

clivemtk
24-03-2011, 08:13 PM
The small klixon will be for the suction bypass if it's a solid state controller and not micro - favoraite on these is 3 way valve passing if it terminates when receiver is front seated that's wat it will be -if it's energised

your age cannot be right are engineers starting young these days

djbe
24-03-2011, 08:41 PM
your age cannot be right are engineers starting young these days

You know that is what I was thinking!

Robert Hilton
24-03-2011, 09:49 PM
You know you are getting old when policemen and fridgie techs look younger than yourself