14-03-2011, 10:48 PM
Hi!
How can I confirm that a hermetic compressor is trash or not (fridge walk in module)? It is running without any noise. Compressor housing is getting warm but piping on pressure side is not increasing mutch. It is not big difference between felt temperatur on pipe for suction or pressure. Suctionpressure is around 5 bar with 134a refrigerant.. Most probably defect compressor that has to be changed out?
Thanks for help.

Brian_UK
14-03-2011, 11:00 PM
5barg = 16°C, not much cooling.

chemi-cool
15-03-2011, 05:10 AM
Compressor is not pumping. No need to check more, replace it.

Sandro Baptista
15-03-2011, 01:55 PM
Does the system have refrigerant on it?

Karlsen
15-03-2011, 08:34 PM
Yes correct amount is verified..

charlie patt
15-03-2011, 08:54 PM
depending on ambient this could be standing pressure whats the run amps of comp?

COBRAKAI
15-03-2011, 09:01 PM
Is the compressor definitely running or is it humming? 5 bar sounds like standing pressure did you manage to take a head pressure reading? If compressor is defo running and not achieving anything would advise to replace

icesav
15-03-2011, 09:56 PM
OK let me throw in my 2 pennies worth... Check that the start relay is ok as a faulty one of these can switch the klixxon inside causeing the comp to overload and just Humm.... Also measure the current across all 3 pins on the comp, start, windings & Ground.