juma
27-02-2011, 02:19 PM
which way is best when pudging air out of the refrigeration system condenser.is it when the compressor is runing or stoped for some time?

monkey spanners
27-02-2011, 02:26 PM
Do you mean a purger like you have in large industrial systems?

Or do you mean when vacuuming a system after repair or when starting for the first time after it is built?

Josip
27-02-2011, 05:33 PM
Hi, Juma :)



which way is best when pudging air out of the refrigeration system condenser.is it when the compressor is runing or stoped for some time?

purging always after .... when is stopped for some time .... what kind of plant we are speaking about ? ... assuming ammonia industrial plant .... there are few hints more ....

Best regards, Josip :)

charlie patt
27-02-2011, 08:18 PM
only purge that i have known you can do is on some of the industrial and transport, befrore our current legislation you are to leave the system of for at least 24 hrs then purge the valve at the highest point on transport on top of the condensor when useing 404 etc and bleed

martinw58
27-02-2011, 08:23 PM
with the system shut down and purge from the highest point

Tesla
27-02-2011, 08:55 PM
juma there have been many posts detailing this operation usually under non condensables. And you can purge any system just not to atmosphere you need to purge into a large empty cylinder.