View Full Version : how to calculate EER ?
ksvinod
09-09-2005, 03:15 PM
Dear all
in aircondtioners how to calculate EER ??
regards
vinod
Argus
09-09-2005, 03:44 PM
Divide the rated output in cooling in kW by the total power input in kW. It will give you a ratio of performance.
You do the same calculation in heating at the design heating condition and it is called CoP.
It is not an indication of true performance, though. Just a benchmark.
________
hemi small block (http://www.dodge-wiki.com/wiki/Dodge_hemi_small_block)
Steve Wright
09-09-2005, 03:50 PM
Basic formula is output BTU/Hr divided by Watts = EER
Example Total net BTU is 93,350 BTUH
Net power 10,740 Watts
93,350/10,740=8.7 EER (BTU per Watt)
Steve
botrous
09-09-2005, 08:20 PM
Hi guys
Check the link below for the calculation of EER and COP
http://www.engineeringtoolbox.com/cop-eer-39_409.html
Technical Requirements for Energy-Using Products EER :
http://oee.nrcan.gc.ca/regulations/html/EERGuide_Part2_3.cfm?text=N&printview=N#9
Hope this helps
Best Regards
ksvinod
10-09-2005, 11:49 AM
thanks dear all
regards
vinod
botrous
10-09-2005, 08:25 PM
Always welcome ksvinod :):):):):):):)