paul_h
21-02-2011, 01:16 PM
Got an old system I changed the compressor in about 2 years ago.
Worked fine until a week ago, now I think the compressor is faulty, any ideas though?
R22 system, recip kirby/tecumseh compressor (AV190TT-051-A4 or AVB5558 EXG - don't know which one is the model# )
36C ambient, went open circuit due to internal temps.
LP 780kPa
HP 1700kPa
These pressures were at the end of the day when taking temp readings after it cut out once already. Before the first cut out and it was cooler, LP was 600kPa and HP was 1500kPa)
indoor air on/off 28/23C
Outdoor air on/off 36/42C
Suction temp 20C
Discharge temp 106C
Capillary heat pump ducted system, no service valves (for example to close liquid line)
Refrigerant was charged by me so nothing wrong with the charge.
Maybe reversing valve, but temps around it don't look too bad:
Reversing valve suc in 21, suc out 24C, discharge in 106C, disc out 102C
Compressor noisier than I would expect, sound under high load, but amp draws were normal (6A per phase, about what you'd expect) Mains voltage was fine too, getting 238V from each phase and 410v across them at the compressor)
Worked fine until a week ago, now I think the compressor is faulty, any ideas though?
R22 system, recip kirby/tecumseh compressor (AV190TT-051-A4 or AVB5558 EXG - don't know which one is the model# )
36C ambient, went open circuit due to internal temps.
LP 780kPa
HP 1700kPa
These pressures were at the end of the day when taking temp readings after it cut out once already. Before the first cut out and it was cooler, LP was 600kPa and HP was 1500kPa)
indoor air on/off 28/23C
Outdoor air on/off 36/42C
Suction temp 20C
Discharge temp 106C
Capillary heat pump ducted system, no service valves (for example to close liquid line)
Refrigerant was charged by me so nothing wrong with the charge.
Maybe reversing valve, but temps around it don't look too bad:
Reversing valve suc in 21, suc out 24C, discharge in 106C, disc out 102C
Compressor noisier than I would expect, sound under high load, but amp draws were normal (6A per phase, about what you'd expect) Mains voltage was fine too, getting 238V from each phase and 410v across them at the compressor)