20-02-2011, 12:03 PM
Hello.
Have a problem with system stopping at lp when cold outdoor temp.
First of all the compressor and condensor is oversized, system designed for 4 walk in cold storage rooms. Today only 2 rooms are in operation.
The compressor only runs for a few minutes before stopping at lp.
To get system running i have to "force" it for about 5 min so the cond pressure builds up and getting liquid back from the condensor. This is only a problem with ambient temp below -20c and last week it has been about -25c -30c outside temp. Only the condensor is located outside with a one way valve on liquid line inside near accumaltor tank. The fans are pressure controled so they dont start at all when this cold.
Would a danfoss kvr solve this problem?
Thanks
Have a problem with system stopping at lp when cold outdoor temp.
First of all the compressor and condensor is oversized, system designed for 4 walk in cold storage rooms. Today only 2 rooms are in operation.
The compressor only runs for a few minutes before stopping at lp.
To get system running i have to "force" it for about 5 min so the cond pressure builds up and getting liquid back from the condensor. This is only a problem with ambient temp below -20c and last week it has been about -25c -30c outside temp. Only the condensor is located outside with a one way valve on liquid line inside near accumaltor tank. The fans are pressure controled so they dont start at all when this cold.
Would a danfoss kvr solve this problem?
Thanks