xeniosavg
18-02-2011, 04:32 PM
I would like to have your comments regarding the possible causes that may lead to the following accident.
A HVAC technician was injured while servicing a Server Room Air Conditioning unit made by LIEBERT HIROSS model Hiflex 4GOA. The injury occurred when the copper pipe between the compressor and the condenser exploded/ruptured. The copper pipe within the condenser which is located outside the building also ruptured violently.
</O:p
The accident occurred while the technician was about to replace the existing refrigerant (R407c) after a low pressure indication and poor performance by the air conditioner. The technician recovered or removed the existing refrigerant (R407c) and then proceeded with the evacuation of the system. As reported the explosion occurred a few minutes after he began the evacuation procedure.
<O:p</O:pThe following equipment was found at the scene of the accident:
<O:p</O:p
A two stage vacuum pump<O:p</O:p
A gauge manifold<O:p</O:p
A Chlorodifluoromethane R22 Cylinder<O:p</O:p
A SUVA 407c Refrigerant
<O:p</O:p
<O:p</O:p
The technician was slightly injured from the copper pipe fragments while the air-conditioning unit suffered a severe damage.<O:p</O:p
A HVAC technician was injured while servicing a Server Room Air Conditioning unit made by LIEBERT HIROSS model Hiflex 4GOA. The injury occurred when the copper pipe between the compressor and the condenser exploded/ruptured. The copper pipe within the condenser which is located outside the building also ruptured violently.
</O:p
The accident occurred while the technician was about to replace the existing refrigerant (R407c) after a low pressure indication and poor performance by the air conditioner. The technician recovered or removed the existing refrigerant (R407c) and then proceeded with the evacuation of the system. As reported the explosion occurred a few minutes after he began the evacuation procedure.
<O:p</O:pThe following equipment was found at the scene of the accident:
<O:p</O:p
A two stage vacuum pump<O:p</O:p
A gauge manifold<O:p</O:p
A Chlorodifluoromethane R22 Cylinder<O:p</O:p
A SUVA 407c Refrigerant
<O:p</O:p
<O:p</O:p
The technician was slightly injured from the copper pipe fragments while the air-conditioning unit suffered a severe damage.<O:p</O:p