PDA

View Full Version : Earthwise Purge



hvacr1
18-02-2011, 12:50 PM
I have to price converting to a new style regerative purge. I was wondereing if anyone has done this. I was wondering how big of a job this is.
Thanks

CV_Geardrive
21-02-2011, 01:18 PM
Hi,
Please let us know what make and model is the chiller, what kind of purge does it have (Purge outlet to evaporator or condenser?), where is located (Beside condenser or in the top of condenser?) and what method has for cooling? (Chilled water or condenser water)
Also please let us know which make and model purge you intend to install.
I have retrofit in the past two LCV and one CVHE from old style to purified purge and I can tell you the procedure.
Regards,
CV

hvacr1
23-02-2011, 02:40 AM
Thanks for the reply. we are changing a eath wise on a CVHE the new regenerating purge has three lines. I was wondering if the vapour supply and liquid return to the condenser can remain the same size or do we have to up size the liquid return to the condenser to 3/8 . I understand that the regereneration line has to go to the evap.
Thanks.
BTW its a air cooled purge

CV_Geardrive
23-02-2011, 12:42 PM
Hi,
Please check your email.
I have sent you a document which, I believe, answers all of your questions.
If not please let me know.
Regards,
CV