17-02-2011, 03:34 PM
We have a site where two RZQ100 condenser coils have failed less than 6 months past 3yr warranty

Has anyone else had issues with their condenser coils dated from 2007>

I know the earlier 2000's were poor but assumed they'd got past that..Aparently not

Cheers

Richard

Tayters
17-02-2011, 06:47 PM
Replaced 1 outdoor unit last summer due to above fault. The coil was leaking about the 4th pass from the bottom. I think the site got some form of Warren G out of it.
A few months later whilst doing a PPM at the site I noted oil around one of the top passes of another unit. Noted it but not sure what happened about it.

They don't make 'em like they used to.

Andy.

still learning
17-02-2011, 09:29 PM
yes , have replaced some on warranty( 1 or2) and some out of warranty.
my first alert to a outdoor coil problem can be oil dripping from the drain bung area underneath to the left of the compressor, they do not always do this .
people who do not have any maintanace may have a good breakdown on the way this summer, the leaks can be tiny and only found after moving the plate where the coils pass thru.
had a dakin wallmout 410a 10 or 12 kw leaking from the small capilleries behind the electrical box, found with a ultrasonic detector