View Full Version : LG LG B48AWYN762 fault code



paul_h
13-02-2011, 09:29 AM
Anyone got a manual or fault codes for an LG LG B48AWYN762?
Got one to look at tommorow, LG have given me authority to repair as the customer can't get anyone out to look at it under warranty.
I have looked at heaps of older LGs in the past out of warranty, but not any new ones, so my info is old. EG they say CH12 fault, and none of my older stuff has that fault code.

install monkey
13-02-2011, 03:01 PM
foun
Error Indicator:




The function provides self-diagnosis and displays an error code if there is any trouble.




Error codes are displayed on the Indoor unit’s Wired Remote as CH**, and/or Fascia Display. In


addition, the code is indicated via LED’s on the outdoor unit control board.




If more than two troubles occur simultaneously, the lower number of error code is displayed first.




After an error occurs, if error is released, error LED is also released simultaneously.


Indoor Unit Faults:


Error


code


Contents Case of error


Indoor


Status


01 Air sensor (open/short) Open / Short circuit Off


02 Inlet pipe sensor Open / Short circuit Off


03


Communication(Indoor

 Wired


R/Control)


Communication Poorly Off


04 Drain pump / Float switch


Float switch Open circuit (High level water


alarm)


Off


05 Communication(Indoor

 Outdoor) Communication Poorly Off


06 Outlet pipe sensor Open / Short circuit Off


07 Different operation mode Indoor units set in different operation modes Off


HL High Limit (Float Switch) Same as code 04, Float switch Open circuit Off


CL Child Lock Function selected


Not an error, press Timer & Min buttons


simultaneously for 3 seconds to toggle On/Off


On


Po Jet Cool Mode selected


Not an error, press Jet Cool button to toggle


On/Off


On


LG Air Conditioning Universal & Multi Split Fault Codes Sheet


Hendra/Macedo - April 2007


- 2 -


Outdoor Unit Faults can also be read from the outdoor unit PCB using the flashing LED’s as below:


Error


code


Contents


LED01G


(Red)


LED02G


(Green)


Case of Error


Outdoor


Status


21


IPM Fault (Compressor Over


current)


2 times 1 time


Compressor malfunction, IPM


Fault


Off


22 CT 2 (Max. Current) 2 times 2 times Current is 14A

 Off


23 DC Link Low Volt. 2 times 3 times DC Link volt. Is 140V

Off


24 Low / High Pressure 2 times 4 times


Low / High press switch


OPEN


Off


25 AC Low / AC High Volts. 2 times 5 times Abnormal AC volt. Input. Off


26 DC Compressor Position 2 times 6 times Off


27 PSC Fault (Reactor) 2 times 7 times Off


28 DC Link High Volts 2 times 8 times Off Off


32 Discharge Pipe Temp. High (INV) 3 times 2 times Off Off


33


Discharge Pipe Temp. High


(Cons.)


3 times 3 times Off Off


40 CT Circuit 4 times CT Circuit malfunction Off


41 D-Pipe sensor INV. (Open/Short) 4 times 1 time Open / Short circuit. Off


44 Air sensor (Open/Short) 4 times 4 times Open / Short circuit Off


45 Cond. Pipe Sensor (Open/Short) 4 times 5 times Open / Short circuit Off


46


Suction Pipe Sensor


(Open/Short)


4 times 6 times Open / Short circuit Off


47


D-pipe Sensor Cons.


(Open/Short)


4 times 7 times Open / Short circuit Off


48 D-Pipe & Air Sensor (Open) 4 times 8 times Dual Sensor unplugged Off


51 Over Capacity 5 times 1 times Over Load Combination Off


52


Communication Error (Main


micom

 Sub micom)


5 times 2 times Poor/Loss of Communication Off


53


Communication Error (Indoor




Outdoor)


5 times 3 times Poor/Loss of Communication Off


54


Outdoor 3-Phase Power Supply


Reverse Phase / Missing Phase


5 times 4 times Incorrect Wiring Off


60 EEPROM Check Sum 6 times Check Sum Mis-Match Off


61 Cond. Pipe Sensor Temp. High 6 times 1 time Cond. Temp. High Off


62 Heat Sink Sensor Temp. High 6 times 2 times Heat Sink Temp. High Off


63 Cond. Pipe Sensor Temp. Low 6 times 3 times Cond. Temp. Low Off


65 Heat Sink Sensor (Open/Short) 6 times 5 times Open / Short circuit Off


67 Outdoor BLDC Fan Lock 6 times 7 times Fan Motor/Circuit Problem Off


105


Comms. Error (Main board

Fan


board)


6 times 5 times Poor/Loss of Communication Off
d some

paul_h
14-02-2011, 12:56 AM
Thanks IM, I've got all the old stuff like that page you tried to copy/paste. Just nothing on the new units/controller, or anything with CH12.

exotiic
14-02-2011, 08:35 AM
Hi Paul, I have a whole range of data on the new stuff, (none on the older).

CH12 Error Code: "EEPROM Sum Check Error - Outdoor unit PCB EEPROM failure, try removing EEPROM and refitting if removable (possible contact fault), otherwise replace the PCB if the EEPROM is non removable.

Edit: Paul can you clear some of your private messages, your inbox is full and I have some further info for you.

paul_h
14-02-2011, 08:53 AM
Done, and thanks.