06-09-2005, 09:54 PM
Hi Guys,
Joy of Joys :rolleyes: , Got called out to a site today to sort out an installation done by another company, i may have seen their horses in the distance as i got there.
Mitsi PKH-1.6 Indoor/ PUH-1.6VKA Outdoor
Both have their own 240v feed going to them with a 3 core link for control
P8 fault (Easy) Outdoor unit :eek: . No Lights on outdoor board. Check Voltage's found 240v between Live and Earth/ 0 volts live to neutal. Checked at input to on/off switch and the same.
now i am assuming therefore lost a neutral at the fusebox. Checked the box, One breaker listing A/C indoor. Switched it off and it kills the power to the indoor and outdoors. Open cover thinking perhaps some cowboy put wires for both units in same breaker (D20 by the way) :eek: only one set of wires, red and black which is what goes into the indoor the only problem is that the wires going to the outdoor are brown and blue.
I am therefore assuming that there must be a connection/spur off that line somewhere between the fusebox and the indoor, cant find anything obvious and am too fat :D to go go crawling around a false ceiling.
Do you come up with the same conclusion as i do or am i having a blonde moment and missing something stupidly obvious :eek:
Regards
Fatboy
Joy of Joys :rolleyes: , Got called out to a site today to sort out an installation done by another company, i may have seen their horses in the distance as i got there.
Mitsi PKH-1.6 Indoor/ PUH-1.6VKA Outdoor
Both have their own 240v feed going to them with a 3 core link for control
P8 fault (Easy) Outdoor unit :eek: . No Lights on outdoor board. Check Voltage's found 240v between Live and Earth/ 0 volts live to neutal. Checked at input to on/off switch and the same.
now i am assuming therefore lost a neutral at the fusebox. Checked the box, One breaker listing A/C indoor. Switched it off and it kills the power to the indoor and outdoors. Open cover thinking perhaps some cowboy put wires for both units in same breaker (D20 by the way) :eek: only one set of wires, red and black which is what goes into the indoor the only problem is that the wires going to the outdoor are brown and blue.
I am therefore assuming that there must be a connection/spur off that line somewhere between the fusebox and the indoor, cant find anything obvious and am too fat :D to go go crawling around a false ceiling.
Do you come up with the same conclusion as i do or am i having a blonde moment and missing something stupidly obvious :eek:
Regards
Fatboy