Hello everyone, Long time lurker....first time poster...so take it easy....:)

I understand TX valve superheating and the reason for it.

My question is ....Would an incorrect superheat setting cause icing up of the evaporater...???

Thanks for your help.....

james10
06-02-2011, 03:47 PM
Yes-not enough refrigerant getting to the evap could cause freezing

sikeston34m
13-02-2011, 07:45 PM
I find this question hard to answer due to not enough information.

Do you have defrost capability on this evaporator? Room Target Temp? Suction Pressure? How is this evap fed liquid?

frank
13-02-2011, 08:00 PM
Hello everyone, Long time lurker....first time poster...so take it easy....:)

I understand TX valve superheating and the reason for it.

My question is ....Would an incorrect superheat setting cause icing up of the evaporater...???

Thanks for your help.....
It would depend on the application.
If you are talking A/C then I would doubt it. Assuming a fully charged system, an incorrect superheat setting (at design conditions) would either result in a flooded evap and liquid returning to the compressor with little or no superheat or evap starvation and a high superheat. As A/C is designed to evaporate around 5C there wouldn't be much sign of frosting. A gas shortage, or restriction would result in evap frosting.